Discuss Odd PME test result... in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Morning guys!

Went to look at a consumer unit change today with a PME supply.

Now, right next to this was an old BS3036 60A fused mem cutout that then sent a pair of 16mm tails to the consumer unit up into the loft, across about 3m and then down the wall in surface trunking down to an old Crabtree CU, with a separate 16mm main earth along side.

Did a Z test at the CU and had a 0.45ohm result, but then the PME cutout had a Ze of 0.47?

I will call the DNO to make them aware, but from what i can see, a BS3036 fuse has an ELI max of 1.07ohms so as this is all well within the limits of the installation, so surely this is ok?

I have no plans to remove the MEM unit and replace with a new one as it is in excellent condition.
 
Probably just a parallel path interfering at the CU but that small difference could be could be the test leads or the meter "seeing it" differently.
Your Ze is theoretically too high for a PME system.
16.0 conductors contained in trunking are undersized for protection by way of a BS3036, 60A fuse.
 
Probably just a parallel path interfering at the CU but that small difference could be could be the test leads or the meter "seeing it" differently.
Your Ze is theoretically too high for a PME system.
16.0 conductors contained in trunking are undersized for protection by way of a BS3036, 60A fuse.
Thanks.

I guess i might need to swap the 3036 for a 50A MCB & enclosure
as there is currently no way to replace the tails that easily!
 

Reply to Odd PME test result... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. New to the forum. I hope I've chosen the correct category to place my post. I tested a landlords property recently, turned out to be TNC. I...
Replies
14
Views
2K
EICR: I’ve come across 30mA RCD supplying a consumer unit via a 63A MCB and 16mm T&E. connected via an isolator to the cutout PME. (Ground floor...
Replies
53
Views
6K
Hi folks, first time poster and soon-to-be landlord's assistant (letting my partner's property out now that she's moved in). We've just had a new...
Replies
70
Views
8K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K
Hi, I'm a recently qualified electrician and my parents need their consumer unit replacing as they are having a new bathroom and they currently...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock