Testing at a house today. The supply is a TN-S. Earth taken from lead incomer cable. First test with my Megger 1730 gave me Ze of 3.5 Ohms, way above the 0.8 Ohms. Cleaned up the earth clamp and tightened it up and improved the reading to 1.7 Ohms. Tested from the live in the fuseboard to the lead sheath of the incoming supply with no earths attached and again achieved 1.7 Ohms. As this Ze value is the best that can be achieved what is my next action. Contact the local DNO and ask them to sort it, or Install an earth rod and change to TT system. This has obviously happened before top some body. Anyone help ------PLEASE.
AdieB
 
Testing at a house today. The supply is a TN-S. Earth taken from lead incomer cable. First test with my Megger 1730 gave me Ze of 3.5 Ohms, way above the 0.8 Ohms. Cleaned up the earth clamp and tightened it up and improved the reading to 1.7 Ohms. Tested from the live in the fuseboard to the lead sheath of the incoming supply with no earths attached and again achieved 1.7 Ohms. As this Ze value is the best that can be achieved what is my next action. Contact the local DNO and ask them to sort it, or Install an earth rod and change to TT system. This has obviously happened before top some body. Anyone help ------PLEASE.
AdieB

Yes call the DNO. It's their earth and they have to maintain it. Don't start making this into a TT, you only need to consider this when no reliable earth has originally been supplied.
 
Bang an RCD in and you will be fine, in the mean time you could contact the DNO and ask them to improve the reading, 1.7 ohms isn't the end of the world and far better than a pin in the ground giving a 30 ohm reading lol.
 
The house is in a residential area. The clamp is an old type which goes around the sheath of the cable with a nut and bolt either side it was slightly loose. I also re-sited it on the cable as did not want to keep tightening and then go bang, this achieved a better Ze. The clamp is fit for purpose just old. There is a 17th edition fuseboard with 100Amp main switch and then two separate RCD's controlling 6 and 4 ways respectively.
 
The house is in a residential area. The clamp is an old type which goes around the sheath of the cable with a nut and bolt either side it was slightly loose. I also re-sited it on the cable as did not want to keep tightening and then go bang, this achieved a better Ze. The clamp is fit for purpose just old. There is a 17th edition fuseboard with 100Amp main switch and then two separate RCD's controlling 6 and 4 ways respectively.

Well what do you think then?
 
I think the DNO should come out and improve the reading. But as I said when I tested from the live in the fuseboard and the sheath of the incoming cable the best I could achieve was 1.7 Ohms so I cannot see how they could give me the required 0.8 Ohms. This is why I have asked the question to see if someone has had this problem before and solved it or advise as to the best way forward.
 
I think the DNO should come out and improve the reading. But as I said when I tested from the live in the fuseboard and the sheath of the incoming cable the best I could achieve was 1.7 Ohms so I cannot see how they could give me the required 0.8 Ohms. This is why I have asked the question to see if someone has had this problem before and solved it or advise as to the best way forward.

But what you cant do is to check the connection back at the sub station can you. Call the DNO, they have a responsibilty to ensure the Ze is within regs.

And yes I have had this on a number of occasions and Western Power sorted it out
 
Yes call the DNO. It's their earth and they have to maintain it. Don't start making this into a TT, you only need to consider this when no reliable earth has originally been supplied.
yes...rodding it will give no real advantage here.....it would be unlikely that TT would give a similar value....and as you say...its distributer earth...so they can sort it....
 
As TaffyDuck has already said fault could be anywhere between mains intake position and sub station. Fault could easily rise way above existing 1.7 ohms. Get DNO out to it. Generally find they respond very quickly to earthing faults on distribution system. Generally couple of hours max.
 
As TaffyDuck has already said fault could be anywhere between mains intake position and sub station. Fault could easily rise way above existing 1.7 ohms. Get DNO out to it. Generally find they respond very quickly to earthing faults on distribution system. Generally couple of hours max.
but he needs to get put straight through to the duty engineer....
not some dopy, obnoxious bint on the end of the phone....
 
Bang an RCD in and you will be fine, in the mean time you could contact the DNO and ask them to improve the reading, 1.7 ohms isn't the end of the world and far better than a pin in the ground giving a 30 ohm reading lol.

So if you were to put RCDs in to meet disconnection times on a TN system that doesn't meet maximum Zs, what I wonder is the position then with certificating the work, particularly in terms of the should-virtually-always-say-None "Deviations from BS7671" box? I know it'd be kosher on a TT system as you have little choice, but on a TN system where Zs is above max...
 
you don't rely on RCDs for disconnection times if at all possible. it's a poor DNO earth. let them sort it, then you can get your testing done.
 
more likely the dozy bint will give you an alternative number that is programmed to play incessant frank sinatra garbage till you get fed up of holding.
 
look, they have a duty to the phone company see...
in future you may be given options to press...
choose from:
.8
.35
21

Then it'll ask you to enter lots of details in order to get you through security checks, ready to be put through to a human being who will then go through all of them again. No, my postcode hasn't changed in the last two minutes, dear.
 
Forget duty engineer IO called Transco for a gas leak and the guy in the call centre could barely talk English not happy with this I called them to say how on earth can anybody report a leak and then said O by the way I had to pay for the call as my mobile provider would not allow a free call and it would also be nice to be thanked a bit like this forum actually
 
that's half the problem with everything today. you sign up for something with a british company, everything is OK and then you get a problem. so you phone the 24 hour help line and get talking to someone who sounds like the punka wallah. can't understand a word.
 
that's half the problem with everything today. you sign up for something with a british company, everything is OK and then you get a problem. so you phone the 24 hour help line and get talking to someone who sounds like the punka wallah. can't understand a word.
Whey thas them caal senta thingys intha toon ye knaa, wu aal talk propa hea an ye cin unastend wu perfect.
 
Last edited by a moderator:
you don't rely on RCDs for disconnection times if at all possible. it's a poor DNO earth. let them sort it, then you can get your testing done.
agreed...its cheap n slovenly..
theres no reason why a well designed system with a stable, reliable means of earthing cannot meet disconnection times without the magic `RCDs`...it bloody well should be doing anyway...
 

Reply to TN-S high Ze in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top