Trunking in house (18th edition)

Discuss Trunking in house (18th edition) in the UK Electrical Forum area at ElectriciansForums.net

peterhyper

-
Esteemed
Reaction score
411
I admit to not taking too much notice of the 18th edition changes as I only took my 18th exam last week (no excuses I am not a good spark like most on here).

I have a flat to do that needs the lighting circuit rewired, but being the ceilings are like concrete and the owners don't want major disruption, it will be done in mini trunking. I usually use self adhesive trunking and seal it with white no nails to give it a strong fixing as drilling through concrete to fix screws in will be an absolute nightmare. So where do I technically stand not using metal fixings to secure it?
 
Unfortunetly you can no longer simply use sticky back trunking for re-wires. The plastic trunking and more importantly the cables in the trunking have to be fixed to the fabric of the building using a metal fixing.
There are many ways to achieve this from purpose made clips to a bit of cut up metal bandy strap.
Either way every single method will require fixing to the ceiling in this case.
Nomore nails glue will not meet the new regs
 
How old is the flat and how is the current wiring run around the flat, did a job with my uncle many years back in a 1920's block and managed to utilise the old conduit and run in singe core cables.
 
How old is the flat and how is the current wiring run around the flat, did a job with my uncle many years back in a 1920's block and managed to utilise the old conduit and run in singe core cables.

Not sure how old the flat is, but I would guess 1940s. The current lighting circuit is in singles and is run inside steel conduit. I always try pulling singles through, but I haven't had much luck with similar set ups in the past.
 
Forgive my naivety, but if I run mini trunking along the ceilings, are the metal fixings to support it supposed to completely cover the mini trunking. The reason I ask is because if the fixings are inside the trunking and a fire started, then the trunking covers would just collapse and the cables fall out?

I appreciate this new requirement is as a result of a very unfortunate incident causing the deaths of firemen, but in reality aren't there many other unsafe practices occurring everyday that are ignored (unless a part pee log is used).

Running 16mm mini trunking in a corner of a room is highly unlikely to trap someone in a building.

Also, if the mini trunking is fitted above the skirting boards, does that also have to adhere to the same criteria in case a person under 6" tall gets trapped under it?
 
Like this Peter ...
10038.jpg
 
Not sure how old the flat is, but I would guess 1940s. The current lighting circuit is in singles and is run inside steel conduit. I always try pulling singles through, but I haven't had much luck with similar set ups in the past.
Any cover plates on the ceilings for the junction boxes or the walls for the sockets?
 
So if I use 100mm wide plastic trunking on a ceiling, the actual cover doesn't have to be secured, so that could potentially catch fire and fall down and trap someone (weighing far more than 16mm mini trunkng).

I think you are missing the point of the change mate.
Try being a firefighter for a day and then see how you feel.
The reg is changed to stop entanglement with cable. This can happen at any height. Feet, arms, heads & breathing equipment can all get entangled. When a house is full of smoke visibility can be virtually non-existent. They may have to feel their way through the house.
 
I think you are missing the point of the change mate.
Try being a firefighter for a day and then see how you feel.
The reg is changed to stop entanglement with cable. This can happen at any height. Feet, arms, heads & breathing equipment can all get entangled. When a house is full of smoke visibility can be virtually non-existent. They may have to feel their way through the house.

I clearly am missing the point. So trunking 6" from the ground above skirting boards has to follow this criteria in case it falls on anyone, and as per my previous post can 100mm plastic trunking covers be fitted unsupported?
 
I clearly am missing the point. So trunking 6" from the ground above skirting boards has to follow this criteria in case it falls on anyone, and as per my previous post can 100mm plastic trunking covers be fitted unsupported?

If you use the word 'entangles' rather than 'fall' then it makes more sense.

Plastic trunking will melt in a fire. It will not entangle a firefighter like copper cable can.
 

Reply to Trunking in house (18th edition) in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock