AdieB

-
Reaction score
6
Hi quick question I have to change a consumer unit out. It is a TT supply system. All breakers will be 61009. I have spoken to my part P tech department and they say that I still need a 100A 100mA S type main switch up front. Another guy says NO as the breakers are all 30mA controls. The first guy said it was required incase there was a neutral fault. But as the neutral also connects into the 61009 will that not provide protection?

AdieB
 
There isn't a requirement as far as know to install an S-type upfront although wouldn't be a bad thing either if you did...the rcbos would have to be double pole or single pole switched neutral.
 
Last edited:
There isn't a requirement as far as know to install an S-type upfront although wouldn't be a bad thing either if you did...the rcbos would have to be double pole or single pole switched neutral.

I was going to use a Lewdon board with RCBO - */30/SP which is single pole but if you look at the diagram it shows that the RCBO coil is looking for out of balance between phase and neutral which would result in a trip. Would this not provide adequate protection?
AdieB
 
I was going to use a Lewdon board with RCBO - */30/SP which is single pole but if you look at the diagram it shows that the RCBO coil is looking for out of balance between phase and neutral which would result in a trip. Would this not provide adequate protection?
AdieB

You shouldn't need the diagram to know that it compares line and neutral!
But no that does not provide protection against neutral faults as it will not clear a neutral fault, only detect it.

Think about what will happen if a neutral to earth fault occurs, the rcbo will detect the flow of diverted current from neutral to earth via the fault and then disconnect the line leaving the diverted neutral current flowing through the fault making it nice and hot ready to start a fire
 
And for that reason a dual RCD board would be better, but surely Dave when the line is disconnected by the individual RCBO, fault current from neutral to earth in that circuit will also cease ?
 
No, because N-E fault current could be from any or all circuits not just the faulty one. The neutrals are all commoned in the busbar and current can just as easily flow out to the fault from the DB as back from the load on the faulty circuit. Hence the need for DP switching to disconnect 'both ends' of the faulty neutral conductor.
 
Last edited:
And for that reason a dual RCD board would be better, but surely Dave when the line is disconnected by the individual RCBO, fault current from neutral to earth in that circuit will also cease ?

The neutral current from that circuit will cease yes, but it will continue to be diverted from the rest of the installation, hence the overheating of the N and E conductors (if it was just the one circuit's neutral current then this wouldn't be an issue)
 
Is there a regulation that says all TT systems with 61009s fitted on all circuits has to have a S type 100A 100mA DP RCD up front. I can not find one. Out of two Napit Tech guys say there is not a requirement. I have also just received a copy of a previous EICR of a job that requires retesting where again it is a TT system with a 100Amp isolator controlling two DP 80A 30mA ( split board) which then controls 60898 mcb's so is this ok as the RCD's are DP? Or should the main isolator be 100mA DP S type as the 30mA will trip before the 100mA
 
Hi AdieB
During my recent NICIEC assessment I was advised to fit a 100mA S type RCD up front on TT systems, because the CUs are now steel and have the additional risk of an internal SC between the flexible conductors that supply the RCDs and earth. It actually states this in the yellow On Site Guide on page 34 below the twin RCD diagram. Two other solutions for TT systems are shown on page 33 - the second showing RCBOs on to a solid busbar not requiring the S type RCD up front.

Cheers
Pete
 
Thanks for the reply I will check my yellow book which is in van. The two boards I am speaking about are both plastic / polycarbon type did your guy say anything about this type of board?
 

Reply to TT Systems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Just a quick sanity check really around rcbo discrimination.. but also RCDs being used as L-E fault protection. Scenario being a garage...
Replies
8
Views
250
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
918
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock