Discuss TT Systems in the UK Electrical Forum area at ElectriciansForums.net
Just reviewed book and if I am reading correctly if you install an AMD 3 metal board on a TT system then you have to install a 100mA 100A rcd external to consumer unit not as a Main switch.
I would phone your CPS technical line and see if they class an RCD as similar switch gear and if they regard it as such then it would have to be housed in a non combustible enclosure so IMO would be pointless installing it externally and may as well swap the main switch for a 100mA s type RCD. I've seen it argued a few times that an RCD may not be classed as similar switch gear as offers no over current protection....IMO I think this is wishful thinking and would have to be housed/enveloped in a non combustible enclosure. I think the general consensus is to take the tails through a purposely made nylon tail gland, adequately support the tails from the board to the meter to minimise movement and replace the main switch for a 100mA S-type to provide earth fault protection to the flexible links that feed the RCD's on a dual RCD board.Just reviewed book and if I am reading correctly if you install an AMD 3 metal board on a TT system then you have to install a 100mA 100A rcd external to consumer unit not as a Main switch.
Just reviewed book and if I am reading correctly if you install an AMD 3 metal board on a TT system then you have to install a 100mA 100A rcd external to consumer unit not as a Main switch.
I have not got my yellow Regs book with me I have the NICEIC site guide page 101. If installed in a TT system there could be a fault between the two incoming tails and the metal casing. Resulting in all exposed conductive parts connected to the main earthing terminal t become live. Due to high external earth fault loop impedance of a typical TT system The service fuse may not operate. Therefore I read it as the RCD must be positioned external to the consumer unit
I have not got my yellow Regs book with me I have the NICEIC site guide page 101. If installed in a TT system there could be a fault between the two incoming tails and the metal casing. Resulting in all exposed conductive parts connected to the main earthing terminal t become live. Due to high external earth fault loop impedance of a typical TT system The service fuse may not operate. Therefore I read it as the RCD must be positioned external to the consumer unit
Reply to TT Systems in the UK Electrical Forum area at ElectriciansForums.net
We use essential cookies to make this site work, and optional cookies to enhance your experience.
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.