If you were to rod the hot tub's panel then it would have to be either isolated from the supply earth by not connecting the cable's earth at the hot tub end (creating its own TT), or you'd run a 10mm bonding cable back to the supply MET.
I'd be happy to have either, (if the TT was of a low value). In this case, I reckon 6 mm of copper, will do an adequate job of protection, even if it's not exactly what the BGB say's!! lol!!
I agree Eng. Just quoting regs really for the op