Search the forum,

Discuss Using pre installed cooker circuit for 13amp or 16amp oven. in the DIY Electrical Advice area at ElectriciansForums.net

Connection unit is OK behind a built in cooker, as long as there's room for it, and it's not in line with any vent the oven has.
 
Yes at moment cooker connection is behind cooker but we are changing it from a freestanding to built in one so it will still be behind oven but oven will be in built in unit will this be ok or as I best asking electrician to move it to the side in one of the cupboards.
That's fine - I assume the existing isolation switch will still be accessible?
 
Was just speaking with wife and she doesn't really like cooker switch on show was just thinking could we get it disconnected and put it in drawer unit next to oven instead of cooker plate so the isolation switch was out of sight or do we still need cooker plate connection as well?
 
It's meant to be easily accessible so that it can be turned off if something happens, such as the oven catching fire or sparking - sometimes people consider putting it in a cupboard acceptable but if there is already one above the worktop I would say it should stay there. You can get nicer looking ones if that is an issue - or reduce it from a double width with socket, to a single switch.

At the very least it needs to be at the front of a cupboard clearly accessible, not where you'd have to reach around or over the oven to get to it and not behind the contents of the cupboard....
 
Thanks for all info I have much clearer idea now. Yes it's just a white cooker switch have never like it but now we're getting it done will leave it were it is and change it for Chrome. Just got last of units out and looking now not sure if there be enough room for cooker connection plate to stay were it is once kitchen unit and oven is in place is it ok to put connection plate inside cupboard screwed to cupboard with a drywall box.
 
Thanks for all info I have much clearer idea now. Yes it's just a white cooker switch have never like it but now we're getting it done will leave it were it is and change it for Chrome. Just got last of units out and looking now not sure if there be enough room for cooker connection plate to stay were it is once kitchen unit and oven is in place is it ok to put connection plate inside cupboard screwed to cupboard with a drywall box.
As long as the back of the cupboard is strong enough to hold it and not the thin plywood, that's fine - it doesn't need to be accessed once the cover is back on until the next inspection or change of oven. Only issue may be routing of cables, but electrician tomorrow should be able to work out the easiest way to do it and still keep things correct...
 
Thanks electrician came out said was ok to keep everything how it is. Just got to wait for oven to be delivered to see what cable oven is supplied with to determine weather it be best to change mcb from 32mcb to 16mcb. Said if it was thinner cable be best to change mcb.I asked about changing 45a cooker switch to 20a as was smaller oven he said no need as 45a is its maximum it will work at lower. Does that sound about right?
 
Thanks electrician came out said was ok to keep everything how it is. Just got to wait for oven to be delivered to see what cable oven is supplied with to determine weather it be best to change mcb from 32mcb to 16mcb. Said if it was thinner cable be best to change mcb.I asked about changing 45a cooker switch to 20a as was smaller oven he said no need as 45a is its maximum it will work at lower. Does that sound about right?
That all sounds fine - the rating of the switch is purely the maximum current it can take so there is no benefit in reducing it. The existing 6mm cable might well be a struggle in most 20A switches anyway..
 

Reply to Using pre installed cooker circuit for 13amp or 16amp oven. in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock