Hi again so oven came today it's has a flex cable on it. It's stamped H05VV-F 3G 1.5. so guessing it's a 1.5mm cable. will a 1.5mm cable be ok to be connected to connection plate that is in wall and just changed MCB to 16amp or would I need get electrician to change cable to 2.5mm as well. Cheers
 
If the oven is supplied with 1.5mm2 cable, then that is fine. If it came without cable, and I was installing it, I'd fit 2.5mm2 by preference, if I thought the terminals would accept it.
 
If the oven is supplied with 1.5mm2 cable, then that is fine. If it came without cable, and I was installing it, I'd fit 2.5mm2 by preference, if I thought the terminals would accept it.
Thanks I did look at 1.5mm amp ratings and some said has rating of 15amp is that true? Would it be better to fit 13amp fuse spur switch to protect cooker cable or not?
 
1.5mm2 cable is within its rating at room temp., but it's likely to be a bit warmer than that behind an oven in an enclosure.
The cable does NOT need protecting against overload, only against short circuit, which the MCB in the CU will do.
Do not run this oven through a 13A fuse for the reasons mentioned earlier in the thread.
 
Thanks for all your help just wanted double check the 1.5mm would still be in 16amp rating were it's warmer behind the oven in a enclosure then?as only installation instructions I could find were from Curry's and of hisense website and they both said hard wire to 13amp fuse spur. Which seems strange for reasons mentioned here. There were no installation instructions with oven only that it was 3.3kw.
 

Reply to Using pre installed cooker circuit for 13amp or 16amp oven. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
995
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
790
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
1K
Good evening, I am new to the forum, and I am after some advice I am looking at buying my son a new oven, but have just noticed that the one I...
Replies
2
Views
2K
Here is my situation We have a dedicated oven circuit in our house with a 40A RCBO We have bought a dual fuel range cooker which states it has a...
Replies
0
Views
885

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock