Search the forum,

Discuss volt drop? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

F

f1ngerz

hi im struggling with volt drop , the circuit is 6mm 2core swa , run under ground , 220M long ,supplying a transformer charging batterys for a gate system rated at 5A.
Can anyone help me and give me the formula for the calculation? Thanks:confused:
 
You need to know load or design current in Amps (Ib), Length in metres (L) and mV/A/m which for 6mm 2core armoured is 7.3.

Then use formula (7.3 x Ib x L) / 1000 = drop in Volts.

(7.3*5*220)/1000 = 8.03. So okay if 5A is your only load and no lights. Max allowable drop is 5% of 230V which is 11.5. Or 3% (6.9V) for lighting.
 
Last edited by a moderator:
Assuming the full 5A as the circuit design current (Ib) the calc is as follows......

VD = mV/A/m x Ib x L / 1000, which using your figures gives us......7.3 x 5 x 220 / 1000 = 8.03A. Surprisingly within the tolerance 5% of 230V which is 11.5V.
 

Reply to volt drop? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock