Search the forum,

Discuss Voltage drop sin phi in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi chaps,
Been working though the electrical design guide and I'm stumped on reactive power. volt drop and the equations are easy enough but I have no idea where sin phi has come from or how they have calculated it at 0.6.

Any help would be greatly appreciated


16762287934246613631673171251362.jpg
 
With small cables at 50Hz, the resistance dominates over the inductive reactance, so the voltage drop due to current flowing along the cable is mostly attributable to the resistance, and the inductive element can be ignored in calculations. As cables get larger, the resistance decreases in inverse proportion to CSA but the inductance does not, so the inductive reactance increasingly plays a part in determining the voltage drop.

Therefore, for larger cables (e.g. 25mm² and up) there are separate figures tabulated for the resistive (r) and reactive (x) components of the voltage drop and the result of the overall impedance (z). The example shows the voltage drop being proportional to the length L, the load current Ib, and the sum of the resistive (r) and reactive (x) components - note the suffixes - multiplied by the cosine and sine of the load phase angle respectively which accounts for the 90° between their contributions to the voltage drop.

Why does the load phase angle play a part? The voltage drop is the effective change in supply voltage that the load sees, but the drop in the cable isn't necessarily in phase with the supply voltage. It occurs as a result of the load current, which is displaced from the supply voltage by the load phase angle Φ. Therefore the magnitude of the drop cannot just be algebraically subtracted from the magnitude of the supply voltage if Φ is significant i.e. if the pf is much below unity.

To summarise:
A load of power factor cos(Φ) draws a current displaced in phase from the supply voltage by Φ.
That current creates a voltage drop in the cable which can be resolved into resistive and reactive components.
For cables over around 16mm², the reactive component is a large enough fraction of the total to deserve consideration.
Tabulated drop figures (r) and (x) are multiplied by cos(Φ) and sin(Φ) respectively and added algebraically to give the total drop.
 

Reply to Voltage drop sin phi in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock