Exactly. A fault condition. A 1A fuse would have blown before a fire situation occurred.It was melting at the switch because of either a defective switch or because of a loose connection.
Discuss Wagos on Final Ring Circuits in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Exactly. A fault condition. A 1A fuse would have blown before a fire situation occurred.It was melting at the switch because of either a defective switch or because of a loose connection.
Are they? Look again!there are perfectly good terminals on the socket..
They do. Look at them. I gave a photo of the bus bar inside them.Wagos are not busbars, they don't have busbars inside,
Nonsense. I, m out.Exactly. A fault condition. A 1A fuse would have blown before a fire situation occurred.
They do. Look at them. I gave a photo of the bus bar inside them.
been connecting socket outlets for years 1, 2 0r 3 if care is taken it will be OK.Are they? Look again!
Using the terminals on the rear of the socket and using non-flexible 2.5mm cable, often means a poor connection. The amount of times I have taken out a socket to find the two 2.5mm cables have moved near out of the connection, or dropped out, is quite a lot. Wagos make a vastly superior connection than shoving two cables into one terminal that could loosen over time or be party dislodged when pushing in the socket using non-flexible cable.
Having Wagos secure the integrity of a ring is a great approach - superb in testing for the 1st fix. Then having flex from the superb connections Wagos give to the socket, with only only one wire connection at the socket, with no chance of the wire being dislodged in the socket connection as flexible wires are used, improves continuity and safety by a considerable measure. Ramming two 2.5mm cables into a socket terminal using non-flexible cable is a real dumb idea.
A win, win, all around. Safer! And quicker.
I think it would be an excellent experiment if you could replicate this fault condition on a lamp switch with a 1A plug fuse and a 10A or 13A plug fuse.Exactly. A fault condition. A 1A fuse would have blown before a fire situation occurred.
The fuse would only rupture if line/neutral or line/earth create a short, this may or not happen and by the time it got to this stage the operation of the fuse may be irrelevant.Exactly. A fault condition. A 1A fuse would have blown before a fire situation occurred.
Exactly. A fault condition. A 1A fuse would have blown before a fire situation occurred.
As someone who is not familiar with the British terminology, may I ask that you use full names instead of initials?A loose connection causes localised heating, but does not cause the current to increase. An AFDD type device would be more likely to break the fault.
Arc Fault Detection Device
John-SJW earlier in this thread in the heat of the moment I made an un-thought-through comment about even current around the ring and was happy to be put right, so you'd be well advised to learn from my experience and pause two marching paces to give thinking time before deciding what is worth saying out loud.Ramming two 2.5mm cables into a socket terminal using non-flexible cable is a real dumb idea.
I am not curious or surprised. Tradesmen are stuck in this we have always done it this way mentality. A resistance to change. Comfofortable with familiar way and products. I have come across this all my life.You must surely be curious as to why so many don't agree with your theories and methods.
Please. ?A loose connection causes localised heating, but does not cause the current to increase.
Only if a short occurred between line/neutral or line/earth and by the time this happens a ruptured fuse may be of no help.Please. ?
The plastic table lamp stand was melting about to burst into flames. A 1A fuse would have stopped it I am sure.
Or may be of help. I would rather have a 1A fuse in a lamps plug than not.Only if a short occurred between line/neutral or line/earth and by the time this happens a ruptured fuse may be of no help.
Please. ?
The plastic table lamp stand was melting about to burst into flames. A 1A fuse would have stopped it I am sure.
I do? New on me, but I will give it a try. When the current is over the rating of the fuse. I got 10/10.You still misunderstand overload current and the reason why a fuse ruptures.