Still having a discussion @ work about this…TNCS system DB/CU is a split 30ma RCD configuration,5/5
MCB’S are 60898 what Max Zs would you put in the column for Max measurement for the MCB😎
 
On a TN system I would normally base it on the MCB Zs value.

Yes, you can disconnect according to regs on 1667 ohms with 30mA RCD, but on TN-C-S it ought to be pretty low and unless it is an unusual situation, anything above the usual OSG sort of tabulated values suggests a fault in the circuit implementation which needs fixing, not a planned use of the RCD.

High current sub-main, or TT earthing, are a very different kettle of fish.
 
Last edited:
Well that’s the dilemma & some disagreement here… To be fair I’ve seen both measurements recorded on Certs… personally I prefer the Zs for the MCB, with the 1666 only for the MCB😎
I personally don't see any value in using the MCB max permitted Zs values when there is an RCD protecting the circuit. Following 411.4.204, table 41.5, and 643.7.1 (a) and (b) means that I don't have to provide a Zs value, either measured or calculated, to prove ADS, assuming I have confirmed continuity of CPC. It frees me up to focus on other parts of the testing.

While I agree that a Zs test might show a problem with a loose connection in the circuit, I find the results to be inaccurate when compared to a continuity test (particularly no trip tests and/or TT earthing). IMO, better to take an R1+R2 reading, which should give a more accurate picture of the circuit's health.

EDIT: it also cuts down on the amount of live testing
 
I would put in the max for the MCB. It is often the case that the RCD does not trip under testing due to no-one ever testing the RCD since it was installed. If the RCD is inoperable I would like to know the MCB will achieve ADS as per regs despite faulty RCD. I have quite often found RCD not operating, a quick few switches on and off "cures" this, but it was faulty until then.
 
I would argue that the RCD component of the circuit is there for additional protection - therefore you'd always use the appropriate Zs to achieve a disconnection time under ADS except if the default stated values by the manufacturer are those for RCD anyway.
 
I would argue that the RCD component of the circuit is there for additional protection - therefore you'd always use the appropriate Zs to achieve a disconnection time under ADS except if the default stated values by the manufacturer are those for RCD anyway.
Yea that’s my thinking, scares me looking @ those 1666 measurements 😎
 
Yea that’s my thinking, scares me looking @ those 1666 measurements 😎
In theory, a max impedance of 1666 on a 230v nominal supply does give you a current of slightly less than 5x but vastly exceeds 1x so it shouldn't matter..... but ..... we press the test button on RCD's for a reason whereas ADS just dependably sits there.

But frankly if you're even anywhere close to working with numbers that high then you've got bigger issues anyway, not least of which is Vd.
 
In theory, a max impedance of 1666 on a 230v nominal supply does give you a current of slightly less than 5x but vastly exceeds 1x so it shouldn't matter..... but ..... we press the test button on RCD's for a reason whereas ADS just dependably sits there.

But frankly if you're even anywhere close to working with numbers that high then you've got bigger issues anyway, not least of which is Vd.
Agree so why would anyone wanna put 1666 in the column regarding TN Systems
Especially when the actual measured Zs is going to be a low Ohm reading
 
If ADS is satisfied by the mcb then use the mcb If ADS is satisfied by the RCD then use that.
I think the technical argument there is that the RCD would be additional protection not basic protection under ADS??

411.x states in several places that where an RCD is used for additional protection it needs to conform to the same ADS times as for Zs measured circuts (paraphrasing!). HOWEVER, 415.1.2. tells us that "The use of RCDs is not recognised as a sole means of protection and does not obviate the need to apply one of the protective measures specified in Sections 411 to 414".

However again, 411.8.3 eventually tells us "where fault protection is provided by an RCD, the product of the rated residual operating current (I∆n) in amperes and the Earth Fault Loop Impedence in ohms shall not exceed 50V". Which as we all know is where we get our magical 1667 * 0.03 = 50v.

On that basis, I think it's probably (as I answer my own theorem...) more technically correct to use the 1667Ω figure in the max Zs column. Still doesn't mean I like it!!! If one of us could be arsed to pick up a GN3 we'd probably find there's a note in there somewhere that clarifies this!! 😂
 
415.1.2 just means if you have an EN 61008 device then you must have an overcurrent device incorporated into it, l believe.
Where an mcb cannot satisfy ADS it is perfectly acceptable to use an RCD and in some circumstances it will provide additional and fault protection.
 
415.1.2 just means if you have an EN 61008 device then you must have an overcurrent device incorporated into it, l believe.
415.1.2 The use of RCDs is not recognized as a sole means of protection and does not obviate the need to apply one of the protective measures specified in Sections 411 to 414.

I think it means that we cannot rely on an RCD alone as a complete protective measure against electric shock.

There are:
411 - Protective measure: ADS
412 - Protective measure: Double/reinforced insulation
413 - Protective measure: Electrical separation
414 - Protective measure: ELV/SELV/PELV,

but there is no section called Protective measure: RCD. This, I believe, is what 415.1.2 is reminding us.
 

Reply to Zs measurements in the Cert column in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock