Discuss Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net
If you have main earth disconnected , surely it would be ZE not ZS.? (at source)
Parallel path via CPC to boiler circuit CPC to boiler manifold to pipework within the fabric of the building?
Also why is the installation energised with the main earth disconnected?
Parallel path via CPC to boiler circuit CPC to boiler manifold to pipework within the fabric of the building?
Also why is the installation energised with the main earth disconnected?
[/QUOTE
working on the HIGGS BOSON PROJECT.Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
You can’t make an omelette without breaking a few eggs.....Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.
Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net