So to answer why I had the circuit energised with the main earthing disconnected..

The lighting circuit connected in board had no CPC so I checked the Zs at a ceiling rose.

I had a reading of 2.2 ohms so I then tried to find out where the earth was coming from.

I disconnected all the CPC's from the other circuit in the board, checked Zs again and still had 2.2 ohms.

Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.
 
Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
 
Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
You can’t make an omelette without breaking a few eggs.....
 
Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.

Why do this as a live test when that means doing something as stupid as energising the installation with the earthing conductor disconnected?

Electricians are supposed to understand the fundamental principles of electrical safety!
 

Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
535
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Replies
7
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top