Search for tools and product advice,

Discuss Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Morning, just checking a lighting circuit on a house, I have the main earth disconnected and still get a zs reading of 2.2 ohms. No evidence of an earth spike and bonding goes direct to henley block.

Any suggestions why this could happen??
 
pics. would help. is you 2.2.ohms a reading from the bonding?
 
I don't understand either. And why would you expect the CPC to be insulated from earth throughout the installation? It could take any value from infinity to zero without indicating anything abnormal. I can see why it might be useful to know for forensic analysis but not for normal testing.
 
So to answer why I had the circuit energised with the main earthing disconnected..

The lighting circuit connected in board had no CPC so I checked the Zs at a ceiling rose.

I had a reading of 2.2 ohms so I then tried to find out where the earth was coming from.

I disconnected all the CPC's from the other circuit in the board, checked Zs again and still had 2.2 ohms.

Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.
 
Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
 
Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
You can’t make an omelette without breaking a few eggs.....
 
Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.

Why do this as a live test when that means doing something as stupid as energising the installation with the earthing conductor disconnected?

Electricians are supposed to understand the fundamental principles of electrical safety!
 
So you've got a circuit with a CPC present in at least one fitting, but no CPC present at the DB, and you want to find out where that CPC is getting its earth from, to decide whether it's trustworthy?

If it were me, I'd turn the board off, maybe separate out the CPCs, null out a nice long wander lead, clip the end of it on the CPC and probe various likely contenders around the house with the meter on low ohms, to see which gives the lowest reading and hence is the likely tap off point. I can't see any advantage investigating this live, but many disadvantages.

Or, since it's at least a bit of a bodge, maybe a lot of a bodge, declare the circuit CPC-less and treat accordingly.
 
Zs is line to earth external impedance, it stands for nothing else.
I understand that but my MFT has those two choices. The KT63 has a piggy back lead that you place the earth lead into to test across L-N I am not truly sure of the purpose of this but there it is. Perhaps you could shed some light on that?
 
Of course there is PSCC and PEFC which I also understand before you go there. I know I should have said loop test. Or PFC PSC even
 
Last edited by a moderator:
Depending on circumstances, main earth may need to be disconnected to verify certain fault conditions..
All comes down to knowledge, understanding what is going on and being in control of the location.
 
Depending on circumstances, main earth may need to be disconnected to verify certain fault conditions..
All comes down to knowledge, understanding what is going on and being in control of the location.

What conditions would they be?
I can't think of any reason to have an installation which relies on ADS energised without its connection to the earthing system.
 
Of course there is PSCC and PEFC which I also understand before you go there. I know I should have said loop test. Or PFC PSC even

Yes it is a loop impedance test which is carried out.
PFC and PSC are not tested or measured, they are calculated by the meter based on the loop impedance and voltage measured at the time.
 
I have also disconnected the main earth to demonstrate to apprentices how parallel earths can appear to drag down the Ze or Zs readings of a TT installation.
I have also disconnected the main neutral to demonstrate how this can be dangerous..
 
Whatever the justification for energising some hypothetical system with the earth disconnected for demonstration or analytical purposes, the OP had a specific task in hand which was to trace a connection to a section of CPC that did not seem to start at the origin. As such, it's a simple continuity test to the MET, other CPCs or mass of earth, that does not require the system to be energised to trace. There is no justification here to work with the system energised.
 
did you finally find the root cause of your problem ? if yes i would appreciate you share it. i have the same. w / wo main Earth wire connected i read same Zs 1.5 ohms. ( TT system) . thank you
 
Neutral/Earth fault causing the reading. But Earth fault loop impedance testing with the Earthing conductor disconnected is stupid and dangerous.

OOPS... Sorry ANCIENT thread!
 
did you finally find the root cause of your problem ? if yes i would appreciate you share it. i have the same. w / wo main Earth wire connected i read same Zs 1.5 ohms. ( TT system) . thank you
I’d start a new thread if I were you and explain why you are doing this in the first place. Only disconnect the main earth to get a Ze reading. Then do dead tests to investigate anything.
A Zs test with the main earth disconnected should never happen.
 
I’d start a new thread if I were you and explain why you are doing this in the first place. Only disconnect the main earth to get a Ze reading. Then do dead tests to investigate anything.
A Zs test with the main earth disconnected should never happen.
I have a TT system ( earth not connected anywhere in any panel with neutral ) and the result i git for Zs was too good to be true . I understood that for a TT system you can not get less than 10 ohms but in my case was 1.5 ohms. I just tested w/o main earth connected to see result..like trying to understand the phenomenon
 
I have a TT system ( earth not connected anywhere in any panel with neutral ) and the result i git for Zs was too good to be true . I understood that for a TT system you can not get less than 10 ohms but in my case was 1.5 ohms. I just tested w/o main earth connected to see result..like trying to understand the phenomenon
I understand what you are asking - you are saying how can the earth path be this good.
It isn't impossible to get a TT Ze of 1.5 ohms, but I agree it's unlikely most of the time.

So to understand what's going on I'd measure the rod specifically by turning off, and disconnecting main earth and loop testing from Live to the wire going to the earth rod.
If you get a better Zs (when it's all back together) then it's usually down to bonded copper service pipes as they make quite good electrodes, and if one of them is connected to a house which isn't TT then there's actually a low resistance path back to the sub-station that way.
Obviously, this can't be relied on, so it's important to make sure the rod itself has a reasonable impedance.

I've had a Zs at the board of 0.4 ohms on a TT system before now (due to bonded services), but the rod was measuring over 400 ohms which I decided was too high so put a new one in.
 

Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
522
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Replies
7
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock