If the cable is clipped direct then it’s fine on a 40amp mcb
It’s when it’s run through floor and roof voids it gets complicated! A 40 amp mcb does not protect the cable , a 32 will, but the load of the shower will cause a thermal effect on the cable and the MCB, HOWEVER both MCB and cable are...
That only applies if clipped direct , none are always underfloor and through roof!
I still think 32 amp MCB is safe until shower circuit is rewired which was the point I was trying to make ?
The problem here is the short time the shower operates for,
Years ago our company added lots of heaters to a ring main in a school, despite me protesting as the QS that it was non compliant, and should be on a dedicated ring or radial circuits, every winter the circuit would trip after about 6...
We do over a thousand tests for local authorities and we can return a C3 as satisfactory with an advisory to rewire the shower as opposed to a C2 failure
It makes a big difference if we send back satisfactory cert! By the way the NICEIC say the 32amp MCB is a C3
trying for a C3 as opposed to a C2 I believe by down rating the MCB and advising our client of the need for it to be rewired when possible we are complying
I agree if new installation , but on an EICR i believe it would be a C2 with the 40 amp mcb and unsatisfactory but with the 32 it would reduce to a C3 and would put a note that needed rewiring when possible?
No need for either in my opinion , as cable needs to be able to take 1.45 rated current without exceeding 60deg C, also MCB will take the current for over an hour