Discuss Shower EICR Code- 9.5kW- 40amp mcb!. De rate MCB to 32 or rewire cable to 10mm in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Trying for a C3? It's either one code or the other!
We do over a thousand tests for local authorities and we can return a C3 as satisfactory with an advisory to rewire the shower as opposed to a C2 failure
It makes a big difference if we send back satisfactory cert! By the way the NICEIC say the 32amp MCB is a C3
 
We do over a thousand tests for local authorities and we can return a C3 as satisfactory with an advisory to rewire the shower as opposed to a C2 failure
It makes a big difference if we send back satisfactory cert! By the way the NICEIC say the 32amp MCB is a C3

Ahh, sorry. I always thought that an EICR was a report on the condition of the installation, and the outcome is based solely on it's condition, not what we want the outcome to be.
 
I attend a rental that some bright person has put a 10kW on a 6mm with 32A mcb. I have advised, but to no avail. I had a close look at the cable (bit I can see), mcb and shower connections and all seems ok, probably more due to use than good design. Strangely they have not asked me for a report :rolleyes: .
 
I attend a rental that some bright person has put a 10kW on a 6mm with 32A mcb. I have advised, but to no avail. I had a close look at the cable (bit I can see), mcb and shower connections and all seems ok, probably more due to use than good design. Strangely they have not asked me for a report :rolleyes: .

Well it works, so what else matters? :(
 
I'm surprised the local authority are not being more causious with this as its a potential fire hazard
 
The problem here is the short time the shower operates for,
Years ago our company added lots of heaters to a ring main in a school, despite me protesting as the QS that it was non compliant, and should be on a dedicated ring or radial circuits, every winter the circuit would trip after about 6 hours , I calculated there was a load of 4 x 12 Amps = 48 amps plus other stuff on the ring yet took 6 hours to trip on a 32amp ring !
 

Reply to Shower EICR Code- 9.5kW- 40amp mcb!. De rate MCB to 32 or rewire cable to 10mm in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
650
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...
Replies
8
Views
3K
Hey all, Could do with some help. I had a company recommended to me who quoted me to do an EICR on my rental property. (£265). I thought this...
Replies
5
Views
2K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock