you really need to be more specific. Basically the IQA has looked at evidence, and not found anything that meets criteria. You can go back to jobs, if it’s within timescale and basically provide evidence to meet gaps.
You hadn’t finished, regardless of assessor comments. That’s the process. My...
I thought smoke alarms are worth noting in report but should not be given classification code. In which case the work would improve the safety but that can be achieved by fitting 10yr battery alarms much cheaper
This is where working OT is a contractual requirement, in which case it is looked at as regular pay and should be pro rata when receiving holiday pay.
It's true as self employed I too don't receive it. But then again I used to pay in one month more tax than I now pay all year on my self...
My zs at db2 from unprotected mcb on db1 was higher than I expected.
With r1/2 on radial socket of .11 I got zs readings of over 8 ohms.
I had dead tested the SWA and had calculated a zs typically at around .4 but hadn't done ze at incoming before energising and taking zs at db2.
Admittedley...
Because they wanted to use summerhouse this weekend.
I normally do tt if house is on PME but don't bother with tns.
Db2 is all RCD protected and RCD tested fine but don't like to rely on RCD to meet disconnection times.
Had high ZE on tns supply @ 3.73ohms
Wired summerhouse and used 40a mcb from db1 with 10mm SWA 3 core on 50m. R1/2 of ..19 to feed Db2 with RCD protected ways.
Checked ze at db1 and got high reading.
Passed to supplier who said will send out team.
Fitted tt earthing at DB2
Supplier asked if I...
It would have been easier to approach client and suggest fire risk assessment. Then any AFD would be installed to the appropriate class.
Just from description that would also include any other amendments e.g basement , shop and flat above with one stairwell should have some building protection...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.