No. My husband is a very good electrician and an inspector and tester. He just wants to make sure he does it correctly. Tell me what this forum is for KAS1 if not for a little help when needed? Im sure my husband has helped people before as he has been thanked by the look of it by other people...
I've got a TNS supply coming into the building with a reading of 0.76ohms. The maximum is 0.8ohms. On circuit one I have a 3phase socket with a reading of 0.88ohms on a breaker60898 C32, maximum permitted for this breaker is 0.72 ohms which is already below my reading of 0.76. How do I make this...
quick question can u cut the neutral and earth fly leads of a rcbo when installing them into a distibuton board so you can make them look somthing? the curly neutral lead is a pain i want to straghten it and cut it to fit is this allowed?:banghead:
sorry i v reposted as i meant yy cable so can anybody tell me why this would be used insted of twin and earth for genral lighting and power as yy is a controll cable and mor expensive than twin and earth.
can i drop cables down 100mm internal metal studded plasterboard walls as someone says i cant becouse the gap cuold be less than 50mm each side of cable, if not what should i do if i cant use rcd on the curcuit.
why would you use yy cable for general lighting and power in a commercial environment over twin and earth, any ideas?
what would be advantages and disadvantages any help would be grateful. thanks sorry yy not sy
when pat testing class 2 equipment do you only have to do a insulation resistance test as a miniumum? or do you have to do more to cover the code of practice
Im looking to get a new 24v sds drill im on a tight budget and yes i want it to last forever lol
does anybody know of any deals or just good buys dont really want to spend more than £350.00 but would do if needed
a panel which is fed by 2x 15o mm 4core armouds which is using the amoring for the eath
has the 2 neutrall conducters tapped up inside the panel as no nuatral is required is thi ok or should they be connected to earth is there a regulation about spare cores or any recomendations help please
who knows of some good online wholesalers, good meaning cheap lol im after swa armoured cable and glands outside sockets and lights any help would be appreciated thanks