Discuss After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch in the UK Electrical Forum area at ElectriciansForums.net

A main switch....not an rcd main switch. A db with a main switch and sp rcbo's would be compliant. It is not the way i would do it though.
Add a s type rcd main switch and the sp rcbo's are no longer compliant.
I wouldn’t add an upfront rcd at all

Dp rcbos with main switch would be much better although not a requirement 🙄
The use of an upfront rcd should be avoided if possible.
 
Last edited:
And - just to throw a spanner in the works!

Regulation 411.5.2 (Just refreshing memory on TT systems) states;
One of the following i) RCD OR ii) Overcurrent Protective Device shall be used, with;

Note 1 "An appropriate overcurrent protective device device may be used for fault protection provided a suitably low value of Zs is permanently and reliably assured."

Now we know in the real world a 'permanently and reliably low value of Zs' is unlikely, but hyperthetically, installing a RCD is not necessarily a god given!
 
And - just to throw a spanner in the works!

Regulation 411.5.2 (Just refreshing memory on TT systems) states;
One of the following i) RCD OR ii) Overcurrent Protective Device shall be used, with;

Note 1 "An appropriate overcurrent protective device device may be used for fault protection provided a suitably low value of Zs is permanently and reliably assured."

Now we know in the real world a 'permanently and reliably low value of Zs' is unlikely, but hyperthetically, installing a RCD is not necessarily a god given!
Irrelevant.
All I have stated is that where an up front rcd is used sp rcbo's would not be compliant. I have not suggested any of the above is required, only the requirements where they are used.
 
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
If something is REQUIRED then that would mean that you MUST use DP rcbos when using an up front rcd, but that's not the case as there are other options to having to use dp rcbos.

Meaning that it's not a requirement.
 
1707778083634.jpeg
 
If something is REQUIRED then that would mean that you MUST use DP rcbos when using an up front rcd, but that's not the case as there are other options to having to use dp rcbos.

Meaning that it's not a requirement.
I have never stated dp rcbo's MUST be used where an upfront rcd is in service, if you read back through my posts I clearly agree other options are compliant such as a dual rcd board.
What I do state (very clearly I believe) and stand by is that wherre rcbo's ARE used......they must be dp where there is a upstream s type rcd and in that arrangement are effectively a requirement, you seem incapable of understanding that I am only refering to where rcbo's ARE used. I believe i have been quite clear that with other arrangements sp rcbo's are compliant.
Perhaps you would be good enough Mainline to answer this.

Lets say you have a job where the designer has specified DB's with rcbo protection to all final circuits. A main switch of s type rcd is also specified. Its a TT earthing system.
Would you install sp rcbo's and provide an EIC on completion?
 

Reply to After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
867
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock