would like your opinions lads on using RCD FCUs
i have come across a few jobs recently where no space at CU or rewireble fuses at CU.client wants all
new spots and extracts etc so i have been taking afeed off upstairs cct to a RCD spur(fused to 5amp) and feeding evrything off bathroom from...
17th says that a lightswitch can be 0.6M from the bath/shower edge as long as it is suitable for its position. - Have any of you heard of anyone getting a shock from a light switch with wet hands?? The Switch is existing and obviously best to fit a pull switch ,- but customer knows not to touch...
Can you still install mains voltage extractor fans in bathrooms? I fitted one the other month but a fellow spark just told me they now have to be low voltage?
Hi,
I am looking for sugestions to comply with 17th ed. when making alterations to circuits (eg lighting) in bathrooms. We now have to have these rcd protected. If its a BS3036 fuse box what would be a good way to provide rcd protection for the lighting circuit.
Ive just wired an extractor fan and pump into the lighting circuit of a bathroom and put an RCD Fuse connection unit in line on the whole circuit, lights and all; the consumer unit in the house is one of the old Wylex fuse ones and I thought that was the easier option rather than trying to put...
adasadas
Thread
bathrooms
canada
circuit
circuits
help
help!
protection
rcd