Hi all. I'm in the market for some testing kit for domestic install purposes and would really appreciate some input as to places to purchase (S London) or online and what models/manufacturers are preffered.
Badly need to upgrade my DMM and was looking into the fluke 11X range
Also not looking...
Hi,
My first post - hope someone can help.
I need to test the prospective fault current at a garage consumer unit. The unit is supplied from an RCBO in the main consumer unit. I intend to carry out the test at the incoming terminals of the garage consumer unit switch with everything switched...
Hi all, have read various threads on this forum regarding PFC measurement but still need a little advice please. Does anyone have a definitive calculation for PFC in ac single phase supplies?
I have just measured PFC in a particular SP domestic installation and I get a reading of 549 amps...
hi all.........need a few pointers
just purchased a 1553 and wondered about the pscc, pefc, pfc measurement?
Am i right in saying that for pscc measurement:
hi pfc range on loop test
red to phase
black to n
pefc measurement:
red to phase
black to n
green to cpc
highest reading is...
Hi all,
I asked the wrong question this morning (it was early) so will try again, If you a have a circuit where you can't easily measure r1 + r2 continuity, such as a circuit to a hob ignition system (no obvious points to probe), is it ok to determine by calculation this measurement using table...
could someone give me some help calculating a circuit resistance for a single phase circuit as it would be entered on a minor works cert if tested?
the circuit in question is a supply from a 2.5mm T&E 30m long going to fused spur then into 1.5 T&E 15m Long.
1st is the calculation done as...
For some reason i keep getting confused about the maxium Zs permitted in the 7671 regs. I have just finished a new rewire on a TT system. The Ze was 14.5 ohms so therefore i assume the Rn is 14.5 ohms. But i am getting confused with what maxium i am allowed on the Zs because when tested at each...
...and see the bosses face!!! he he
VINTAGE MEGGER UNIVERSAL EARTH RESISTANCE TESTER on eBay, also Meters, Test Measurement Equipment, Electrical Test Equipment, Business, Office Industrial (end time 22-Nov-08 20:13:05 GMT)
sivoodoo
Thread
earth
electrical work
equipment
measurement
resistance
tester
these