Come across an old Installation with 1.5mm CPC on a 6mm Live conductors whilst doing an EICR. Not seen many of these, in everyones opinion perfectly acceptable if all R1 and R2, IR, Measured ZS test check out ok?
Discuss 1.5mm CPC on 6mm Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Come across an old Installation with 1.5mm CPC on a 6mm Live conductors whilst doing an EICR. Not seen many of these, in everyones opinion perfectly acceptable if all R1 and R2, IR, Measured ZS test check out ok?
I find it difficult to believe 6.0 T&E was produced with a 1.5 cpc, four times smaller than the csa of the line conductor.
Yes I made the assumption T&E in #5 after he used the word cable in #3 but plenty of people refer to a single conductor as a cable so who knows.The OP hasn't confirmed what type of cable it is, I assume it is most likely singles.
Reply to 1.5mm CPC on 6mm Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net