- Reaction score
- 0
10/3 120ft. Going to an out building. Black and red On 1 breaker to keep amps up. What is the max breaker for that setup?
Discuss 10/3 120ft. Black and red On 1 breaker to keep amps up. What is the max breaker for that? in the USA Electrical Forum area at ElectriciansForums.net
On the busbar with like normalWhat are you doing with the return (neutral)?
Yes. I had the 10/3 already. And just trying to reduce the amperage fade off. I was going to use a 15 or 20 breaker. But wanted someone else’s opinion on the breaker size and if I need to go bigger or could go bigger what y’all suggested. I think it would be fine with a 20 amp breaker but I’m curious as to what y’all would doOk, but don’t forget that if you double the conductors to the breaker (to allow for larger current?)
Then you have to double the conductors on the neutral as well.
The current on the neutral will be the same as on the live.
I can double the neutral if I need to with no problemOk, but don’t forget that if you double the conductors to the breaker (to allow for larger current?)
Then you have to double the conductors on the neutral as well.
The current on the neutral will be the same as on the live.
If you double the current on one side of the circuit you MUST double the other side as well. If you don’t increase the neutral then it will melt when the increased (double) load goes through it.I can double the neutral if I need to with no problem
If you double the current on one side of the circuit you MUST double the other side as well. If you don’t increase the neutral then it will melt when the increased (double) load goes through it.
Not sure why you need to increase your cable size. Is it a bigger load, or is it to reduce volt drop?
I am in the UK and so I have no idea what the characteristics are of 10/3 cable. But the principles of circuit currents are the same everywhere. You must double both legs. Probably the earth too, as the earth fault path may not meet code.
First off thank you for responding to my inquiry. But…. I under stand what your saying. I did say amp drop off In my earlier reply but I meant volt drop off. Ok. So all I want to know is the max breaker so I do not burn up my wiring. I want to make sure I stay well under the max. If you don’t understand the wire I am using then you don’t know what the max breaker I can use. So saying that, you can not answer my original question. And if you can’t answer my original question then why are you even commenting at all?If you double the current on one side of the circuit you MUST double the other side as well. If you don’t increase the neutral then it will melt when the increased (double) load goes through it.
Not sure why you need to increase your cable size. Is it a bigger load, or is it to reduce volt drop?
I am in the UK and so I have no idea what the characteristics are of 10/3 cable. But the principles of circuit currents are the same everywhere. You must double both legs. Probably the earth too, as the earth fault path may not meet code.
Just pointing out a general issue in your plan and hoping you take that on board.First off thank you for responding to my inquiry. But…. I under stand what your saying. I did say amp drop off In my earlier reply but I meant volt drop off. Ok. So all I want to know is the max breaker so I do not burn up my wiring. I want to make sure I stay well under the max. If you don’t understand the wire I am using then you don’t know what the max breaker I can use. So saying that, you can not answer my original question. And if you can’t answer my original question then why are you even commenting at all?
30 amp breaker10/3 120ft. Going to an out building. Black and red On 1 breaker to keep amps up. What is the max breaker for that setup?
Reply to 10/3 120ft. Black and red On 1 breaker to keep amps up. What is the max breaker for that? in the USA Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.