If you are saying you have an extension lead that can take 10A and the battery charger only draws 7A then it will be ok, from a current carrying capacity.
If the extension lead is coiled up while you are using the charger then heat from the coiled up extension lead may cause a problem.

Oh.... and, welcome to the forum mate...
 
what he says. ^^^^^^. if its a coiled lead, unwind before use unless you prefer it melted.
 
If you are saying you have an extension lead that than take 10A and the battery charger only draws 7A then it will be ok, from a current carrying capacity.
If the extension lead is coiled up while you are using the charger then heat from the coiled up extension lead may cause a problem.

Oh.... and, welcome to the forum mate...
Thank you. Yes, the extension lead is rated 10 Amps and will be used laid out flat/fully extended with a CTEK 12 Volt/7 Amp Charger.
 
hang on.that 7A is probably the current at 12V. the current drawn through the 240V lead will be 7/20.
 
The charger almost certainly outputs at 12v, 7A. The 230v input supplies an isolating transformer from which the 12v is derived. The current on this 230v supply will be nowhere near 7A, the 7A is the output only.
 

Reply to 10 Amp Extension Lead in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm a hobbyist without formal training. I'm looking to power audio/video equipment over several hundred feet of extension cords. I have 2...
Replies
4
Views
378
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
830
Hi Guys. Is it safe to use an extension lead with a single pin 48V battery charger for an e-trike? The charger has a standard UK 3-pin mains plug...
Replies
5
Views
857
I am looking for advice on getting an upgraded 25 meter extension cable from my office into my car park to charge my EV from an IP66 rated socket...
Replies
7
Views
2K
I have Liebherr fridge freezer and need to extend the cable from the appliance to the wall plug. The directions do not allow an extension lead to...
Replies
2
Views
844

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock