Search the forum,

Discuss 100 Amp Service in the USA Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello all,

I am looking to run 1.5 conduit underground 100 feet to my garage. I want 100 amps of electrical service - 2-2-2-4 wire URD or should I look at copper? WOuld copper 4-4-4-6 support it?

I am not worried about code because I am away from all that - but I don't want to burn my house down.
 
Hello all,

I am looking to run 1.5 conduit underground 100 feet to my garage. I want 100 amps of electrical service - 2-2-2-4 wire URD or should I look at copper? WOuld copper 4-4-4-6 support it?

I am not worried about code because I am away from all that - but I don't want to burn my house down.
100 amp requires # 3 wire copper and since you already have a conduit installed if I was you I would pull three # 3 THHN copper wires and one # 6 ground copper. It’s a little more expensive but a whole lot easier to work than aluminum but. Good luck
 
100 amp requires # 3 wire copper and since you already have a conduit installed if I was you I would pull three # 3 THHN copper wires and one # 6 ground copper. It’s a little more expensive but a whole lot easier to work than aluminum but. Good luck
Since you don’t care about the code # 4 copper would work because you will probably never pull 100 amps
 
# 3- 110 amps copper # 4 90 amps copper
My advice is to do it right with at least 125 amp main lug only panel installed in your garage. That’s a lot of amperage and your own house doesn’t probably worst case pull 50 amps at one time. I’ve wired MANY garages and buildings and usually just pull # 8 copper and never had a complaint. Your not going to burn your house down. I think that since you are a DIY you need to at least consult an electrician. There’s many things in the NEC that your not aware of and safety is the upmost importance.
 
I keep seeing this come up Al MHF wire:

I like the price - I want a main disconnect in the garage as well - Can I run this in conduit? Anything wrong with the wire other than its aluminum? Any box recommendations? I need maybe 6-10 circuits, thinking a 90mp breaker.
Or should I go copper - and if so, what gaige 4-4-4-6? The alumnium is just so much more affordable.
 
I keep seeing this come up Al MHF wire:

I like the price - I want a main disconnect in the garage as well - Can I run this in conduit? Anything wrong with the wire other than its aluminum? Any box recommendations? I need maybe 6-10 circuits, thinking a 90mp breaker.
Or should I go copper - and if so, what gaige 4-4-4-6? The alumnium is just so much more affordable.
My friend just go with the aluminum it’s just a personal preference so instead of a main lug only panel buy one that already has a main breaker in it. They have 12 circuits and 26 circuits at Home Depot and Lowe’s. The breaker that’s already in it will be probably a 125 amp breaker, just replace it with a 90 amp double pole breaker. Yes you can pull either Aluminum or copper in a 11/2 conduit
 
It sounds like the garage is detached so unless having 6 or fewer circuits, a main will be required + a grounding electrode, such as a Ufer, AKA a concrete encased electrode, or a couple of ground rods driven at least 6 feet apart.
 
It sounds like the garage is detached so unless having 6 or fewer circuits, a main will be required + a grounding electrode, such as a Ufer, AKA a concrete encased electrode, or a couple of ground rods driven at least 6 feet apart.
NorCal you are not required to have ground rods on a sub fed panel. All the bonding takes place at the main service panel. You have to pull 4 wires to the building and add a ground bar if it doesn’t have one and isolate the grounds from the neutrals.
 
NorCal you are not required to have ground rods on a sub fed panel. All the bonding takes place at the main service panel. You have to pull 4 wires to the building and add a ground bar if it doesn’t have one and isolate the grounds from the neutrals.
If in the same structure then not required, but in a separate structure yes they are required, just no bond between the neutral & grounding conductor in the subpanel, & the grounding electrode conductor would land on the ground bar.
 
If in the same structure then not required, but in a separate structure yes they are required, just no bond between the neutral & grounding conductor in the subpanel, & the grounding electrode conductor would land on the ground bar.
You will need to find the article in the NEC which you should know is article 250 of the NEC
 
See 250.32(A)
Your close but read the exception to that particular article. That’s why I say pull 4 wires with one of them being the grounding conductor from the main panel. Think about it you don’t need ground rods at the building because you already have it through your equipment ground.
 
The exception is for a single branch circuit, including a multiwire branch circuit, a feeder still requires a electrode. The exception makes sense when you want to have a 20A circuit to a shed for a light, and/or receptacle(s), for example. Unless somebody was under a very old NEC, a 4-wire feeder is required, code permission for 3-wire feeders is long gone & a grounding electrode is still required for a separate structure unless a single branch circuit.
 
The exception is for a single branch circuit, including a multiwire branch circuit, a feeder still requires a electrode. The exception makes sense when you want to have a 20A circuit to a shed for a light, and/or receptacle(s), for example. Unless somebody was under a very old NEC, a 4-wire feeder is required, code permission for 3-wire feeders is long gone & a grounding electrode is still required for a separate structure unless a single branch circuit.
I can tell that you haven’t dealt with any inspectors. I’ve wired many buildings and garages and I have never drove a ground rod at any of them and I haven’t felled inspection. Let’s move on and quit arguing and we will agree to disagree
 

Reply to 100 Amp Service in the USA Electrical Forum area at ElectriciansForums.net

Similar Threads

I am working on a RV Park and I have a question. I plan on installing 4/0 quadraplex AL URD cable to 10 pedestals on a 200 amp circuit and...
Replies
0
Views
239
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
575
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
628
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
489
I am adding a 60 AMP subpanel for a detached garage/workshop with a 200 foot underground conduit run from the main panel to the sub panel...
Replies
3
Views
986

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician State Laws for Electrics and Electricals may differ on a state-by-state basis. American questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top