Discuss 100mA time delay rcd in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
7
Hello guys,

I'm after a bit of advice/opinion on this one.

A customer has a plumis mist sprinkler system that needs power.

I'm planning to stick in a separate unit, 100mA time delayed rcd as he wants the cables buried. If I just stick a mcb off of that would that be acceptable? It's not a TT system but it's what's suggested in the manufacturers instructions.

I'm not too clued up on time delay stuff so would appreciate any input.

Cheers
 
Hello guys,

I'm after a bit of advice/opinion on this one.

A customer has a plumis mist sprinkler system that needs power.

I'm planning to stick in a separate unit, 100mA time delayed rcd as he wants the cables buried. If I just stick a mcb off of that would that be acceptable? It's not a TT system but it's what's suggested in the manufacturers instructions.

I'm not too clued up on time delay stuff so would appreciate any input.

Cheers

For the cables to be buried at a depth below 50mm in prescribed zones you would require 30ma RCD protection
 
Doesn't have to be 100mA tbf, couldn't find a time delayed 30mA rcd so was an assumption off of left field I guess. Was going to use t and e to a fused spur from the CU and buried in the wall.


Well it needs 30mA rcd protection unless it complies with the reg I posted earlier. I would be looking at alterantive methods of installation to do away with RCD protection on a system loke this unless tye MI states it needs one.
 
Well it needs 30mA rcd protection unless it complies with the reg I posted earlier. I would be looking at alterantive methods of installation to do away with RCD protection on a system loke this unless tye MI states it needs one.

Yeah would be less hassle if he'd have it surface but doesn't want it. MI suggested time delayed rcd as only viable option if buried in wall.
 
A 30mA time delayed RCD wouldn't help as the regulation requires a standard 30mA RCD.

Some foil screened (but not all) cables comply with the requirement for an earthed metallic surround/sheath or whatever. FP200 is one example of this
 

Reply to 100mA time delay rcd in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Having to wire around a messed up output for a month or so. Some sort of program corruption is keeping the central lubrication system from...
Replies
3
Views
826
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
985
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
922
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
890

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock