Discuss 110v 20amp circuit using existing #8 Alu wiring to 40amp breaker. in the UK Electrical Forum area at ElectriciansForums.net

MikiSJ

DIY
Reaction score
0
I am abandoning an oven/microwave location that has an existing 220v 40amp (4-wire) circuit. I am leaving the wiring in place. I want to use the new counter space for a built-in microwave oven and coffee station.
Can I use one of the 110v circuits in the junction box for a 110v 20amp receptacle and also another 110v 20amp circuit? The wire from the existing 220v wiring to the new 110v circuits will be inches?
Or, should I install a small load center?
 
I am abandoning an oven/microwave location that has an existing 220v 40amp (4-wire) circuit. I am leaving the wiring in place. I want to use the new counter space for a built-in microwave oven and coffee station.
Can I use one of the 110v circuits in the junction box for a 110v 20amp receptacle and also another 110v 20amp circuit? The wire from the existing 220v wiring to the new 110v circuits will be inches?
Or, should I install a small load center?
The biggest problem I see is you will have to share the neutral with 2 different phases which is not allowed
 
The biggest problem I see is you will have to share the neutral with 2 different phases which is not allowed
Thank you for your reply. Why would this be different than using a 3-wire circuit where the black goes to the top of a receptacle and the red to the bottom of the receptacle where the top/bottom is switched?
 
Thank you for your reply. Why would this be different than using a 3-wire circuit where the black goes to the top of a receptacle and the red to the bottom of the receptacle where the top/bottom is switched?
If you share a neutral on let’s say say A phase and no problem but you have a problem with the B phase for what ever reason and you take the neutral loose it can shock you since A phase ie also using the same neutral which will have some power on it. Sorry
 
WARNING - Homeowner and electrical engineer and not an electrician (though my grandfather and uncle are)

Isn't the OP just proposing turning the existing 40A circuit into a multiwire branch circuit (MWBC) - two hots on opposite phases sharing a neutral? Breaker would need to be changed out to 20A two pole (assuming the existing wiring can fit into the 20A breaker) with a common trip/handle tie, but that should be legal, right?
 
WARNING - Homeowner and electrical engineer and not an electrician (though my grandfather and uncle are)

Isn't the OP just proposing turning the existing 40A circuit into a multiwire branch circuit (MWBC) - two hots on opposite phases sharing a neutral? Breaker would need to be changed out to 20A two pole (assuming the existing wiring can fit into the 20A breaker) with a common trip/handle tie, but that should be legal, right?
Bingo you are right but the OP wanted to continue to use the 40 amp double pole breaker and share the neutra.
 

Reply to 110v 20amp circuit using existing #8 Alu wiring to 40amp breaker. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
906
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
838
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
486
Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Replies
19
Views
2K
Currently I have a 20AMP breaker with 12 gauge wire going to a 15AMP GFCI receptacle in a bathroom. The receptacle is the only item on this...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock