Have you spoken the the rewinder, did they rewind as it was originally?
Is it 6 wire single speed?
Why did it need to be rewound, have the contactors or contacts been replaced?
 
Can you post a picture of the nameplate on the motor, if it can be done safely, a pic of the motor wiring terminals would be good to.
 
When a motor fails you need to establish the root cause, it is quite possible the motor failed because of a control issue so regardless of the rewinding been done correctly you may be subjecting it to the same issue that saw the original demise.
Have you done any testing to confirm voltages etc off and on load, also what is the starting method and what is the nature of the motor.
As above the nameplate will give us a start.
 

Reply to 125 HP motor speed problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a project I have been working on, that has me out of my depth with regard to my knowledge, as I am a very basic electronic hobbies...
Replies
5
Views
1K
hello, i have a central AC Fan Coil with a 3 speed motor within my Condominium. I run the fan of low but find it blows too much air and produces...
Replies
1
Views
717
Hi, First of all I must explain why my posting came to be on this site, I was looking on the internet for a forum that could help with a project...
Replies
8
Views
1K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock