Hi I've installed a 12v ac relay but the 12v supply won't pull the relay coil in. It gets it signal from a disabled alarm kit. Multimeter shows a healthy 12v when alarm is activated but relay won't energise. Tried a couple of different relays but no joy. ????
 
check that the relay is a 12v coil.
 
You dont indicate what you are switching with the relay ? remember the alarm 12vac wil be jus enough to switch the electronics

More information is required
 
Make sure the coil is not too big for the supply it could be you have the right coil but the supply 12v may not be big enough

You'd get some clue by looking at the voltage across the coil when its energised. If it's significantly lower than 12V, say less than 10V, then you may need a relay with a higher coil resistance. The relay spec sheet should say what the minimum voltage for pull-in is.
 

Reply to 12v ac relay not pulling in in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I’m stumped and can usually figure it out after a while but not on this one. so I joined here In search of some help on my 05 tundra I’m...
Replies
1
Views
890
Hi - On our small vessel we have a 12v failry powerful motor to run the autopilot, where the power is supplied by the boat's battery bank. On an...
Replies
20
Views
2K
Hi all. I'm trying to put a light-bar on my (facelifted) Land Rover Freelander 2. I'm wanting to wire it so the light-bar will be energised when I...
Replies
9
Views
966
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Hi I am reconfiguring a hot wash unit and need to use a flow switch as in attached files. It controls a light powered relay and timer module I...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock