4.8kW is around 21 amps. 3.7kW is around 16 amps. I'm not sure where you are getting those figures from.

Also, 6mm² flat twin and CPC cable is able to carry 47 amps, but only if clipped direct.
If it's in trunking, or passes through any insulation for any of its length, then it can severely reduce the capacity to well below 40 amps. It may be necessary to replace the 40 amp breaker with a 32 amp breaker.

That being said, after applying diversity that is normally allowed for cooking appliances, the total load would work out at around 18 amps.
 
4.8kW is around 21 amps. 3.7kW is around 16 amps. I'm not sure where you are getting those figures from.

Also, 6mm² flat twin and CPC cable is able to carry 47 amps, but only if clipped direct.
If it's in trunking, or passes through any insulation for any of its length, then it can severely reduce the capacity to well below 40 amps. It may be necessary to replace the 40 amp breaker with a 32 amp breaker.

That being said, after applying diversity that is normally allowed for cooking appliances, the total load would work out at around 18 amps.
Thanks Loz.

The amps I stated are taken from the seller's website against "Amperage".

The 6mm cable runs from the CU through a wall and then is clipped to a wall (underneath cabinets prior to going up through a dot and dab wall cavity to an oven switch.

It sounds like the existing circuit will be sufficient to power both of these. There is a plug on the cooker switch, will this also be OK? So supply to the oven, hob and single socket will suffice?
 

Reply to 13A hob and 32A oven on same circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
666
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
I note that in answer to another EV Charger question a member suggested a 40A breaker would be preferred to a 32A because of many hours at...
Replies
34
Views
2K
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock