Search for tools and product advice,

Discuss 14-50R ground/neutral question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Question: Do I tie both the ground and neutral to the same bar in the panel (on the right in the photo)?

Explanation: I am installing an outdoor 14-50R receptacle to power a travel trailer on my property. The previous owners had one installed but the receptacle and UF wire was removed by the previous owners or stolen while the home was vacant.

Im using 6/3 UF wire for the run. The trouble I'm having is where to tie the neutral into the breaker panel. There is no neutral bar in the box (as far as I know). The 200 amp breaker panel is directly below the meter and still has the 50 amp breaker in place. I have included a photo of the box.

Disclaimer: Yes, I can see the panel is a mess, the unattached exposed wires are not hot and I will remove them when I have the time. I know to shut off the main breaker when removing the panel cover. I have a fair understanding of electricity and the consequences of being reckless, unfortunately I just do not have the money to have an electrician do the install. My grandfather lives with us and is a retired industrial electrician and has told me his opinion but his mind has been deteriorating and I can't trust his advice.

20190909_122721.jpg
 
Thank you. I do not find the diagram helpful or informative. I will find the solution elsewhere.
CJ is this panel outside w
Question: Do I tie both the ground and neutral to the same bar in the panel (on the right in the photo)?

Explanation: I am installing an outdoor 14-50R receptacle to power a travel trailer on my property. The previous owners had one installed but the receptacle and UF wire was removed by the previous owners or stolen while the home was vacant.

Im using 6/3 UF wire for the run. The trouble I'm having is where to tie the neutral into the breaker panel. There is no neutral bar in the box (as far as I know). The 200 amp breaker panel is directly below the meter and still has the 50 amp breaker in place. I have included a photo of the box.

Disclaimer: Yes, I can see the panel is a mess, the unattached exposed wires are not hot and I will remove them when I have the time. I know to shut off the main breaker when removing the panel cover. I have a fair understanding of electricity and the consequences of being reckless, unfortunately I just do not have the money to have an electrician do the install. My grandfather lives with us and is a retired industrial electrician and has told me his opinion but his mind has been deteriorating and I can't trust his advice.

View attachment 52025
CJ is this panel outside with or beside the meter ?
[automerge]1568059164[/automerge]
View attachment 52027their you go ,ten million words .
Another good schematics by Buzz
[automerge]1568060160[/automerge]
CJ The NEC states that the first disconnect after a transformer which is your panel you have to bond the panel to the neutral bar so you can hook up both your neutral and your equipment ground any panel is sub-fed from that panel then you have to isolate your grounded conductors and your grounding conductor ALLWAYS DISCONNECT ALL POWER ( turn main 200) I seen you had the turned off the main to take the cover off and that’s the best advice I can give you
 
Last edited:
I start with the disclaimer that I am a UK electrician and my knowledge of USA wiring practice is very basic.

However it appears to me that something isn't quite right here, normally the white conductor is the neutral in the USA however they are connected to breakers here. It doesn't look like the breakers are connected to the neutral bar to work double pole so I assume they are following the normal US arrangement of being connected to the two lives.
So my suspicion is that cable intended to carry live, neutral and ground has been used to carry two lives and the ground is being used for both neutral and ground.

As far as I understand it this is not allowed.
 
I start with the disclaimer that I am a UK electrician and my knowledge of USA wiring practice is very basic.

However it appears to me that something isn't quite right here, normally the white conductor is the neutral in the USA however they are connected to breakers here. It doesn't look like the breakers are connected to the neutral bar to work double pole so I assume they are following the normal US arrangement of being connected to the two lives.
So my suspicion is that cable intended to carry live, neutral and ground has been used to carry two lives and the ground is being used for both neutral and ground.

As far as I understand it this is not allowed.
Dave all neutrals connect to the neutral bar in the panel the only neutrals that connect to single pole breakers and double pole breakers are GFCI breakers which the neutral connects to the breakers then the breakers have a what I call a pig tail that connects to the neutral bar. If you are referring to my previous statement about the neutrals and grounding conductors connected to the same bar. That is only done at the first disconnect after the transformer but if you subfeed any panels out of the first panel you have to separate the grounding conductors from the neutrals conductors
[automerge]1568069669[/automerge]
Dave all neutrals connect to the neutral bar in the panel the only neutrals that connect to single pole breakers and double pole breakers are GFCI breakers which the neutral connects to the breakers then the breakers have a what I call a pig tail that connects to the neutral bar. If you are referring to my previous statement about the neutrals and grounding conductors connected to the same bar. That is only done at the first disconnect after the transformer but if you subfeed any panels out of the first panel you have to separate the grounding conductors from the neutrals conductors
Dave if we have a piece of equipment that requires a neutral we generally pull a 3 wire cable a with ground. They are times when we have 240vac piece of equipment that don’t require a neutral we can pull a two wire cable with ground and the white can carry lives as long they are phase taped on both ends so there won’t be any confusion
[automerge]1568069938[/automerge]
Dave all neutrals connect to the neutral bar in the panel the only neutrals that connect to single pole breakers and double pole breakers are GFCI breakers which the neutral connects to the breakers then the breakers have a what I call a pig tail that connects to the neutral bar. If you are referring to my previous statement about the neutrals and grounding conductors connected to the same bar. That is only done at the first disconnect after the transformer but if you subfeed any panels out of the first panel you have to separate the grounding conductors from the neutrals conductors
[automerge]1568069669[/automerge]

Dave if we have a piece of equipment that requires a neutral we generally pull a 3 wire cable a with ground. They are times when we have 240vac piece of equipment that don’t require a neutral we can pull a two wire cable with ground and the white can carry lives as long they are phase taped on both ends so there won’t be any confusion
I would never allow 1 wire to serve 2 purpose
[automerge]1568070251[/automerge]
Dave all neutrals connect to the neutral bar in the panel the only neutrals that connect to single pole breakers and double pole breakers are GFCI breakers which the neutral connects to the breakers then the breakers have a what I call a pig tail that connects to the neutral bar. If you are referring to my previous statement about the neutrals and grounding conductors connected to the same bar. That is only done at the first disconnect after the transformer but if you subfeed any panels out of the first panel you have to separate the grounding conductors from the neutrals conductors
[automerge]1568069669[/automerge]

Dave if we have a piece of equipment that requires a neutral we generally pull a 3 wire cable a with ground. They are times when we have 240vac piece of equipment that don’t require a neutral we can pull a two wire cable with ground and the white can carry lives as long they are phase taped on both ends so there won’t be any confusion
[automerge]1568069938[/automerge]

I would never allow 1 wire to serve 2 purpose
With all this said we are mostly talking about single family dwellings using NM cable. On most jobs I did we always had to run pipe then pull singles and no problem. With wire colors
 
Last edited:
Dave all neutrals connect to the neutral bar in the panel the only neutrals that connect to single pole breakers and double pole breakers are GFCI breakers which the neutral connects to the breakers then the breakers have a what I call a pig tail that connects to the neutral bar. If you are referring to my previous statement about the neutrals and grounding conductors connected to the same bar.

I'm not talking about your previous statement, I'm talking about the photo in the opening post.
There are three large wires coming in which I assume are the two lives and neutral. What I assume is neutral goes to a terminal bar with a link to the metal case I understand that this is where you normally make a N-earth link in the US so seems fine to me. However I don't see any seperate ground terminal bar in the picture.
What I don't get is that all of the bare copper conductors which I understood to be ground then connect to what appears to be the neutral bar, while the black and white wires connect to the DP breakers.
 
I'm not talking about your previous statement, I'm talking about the photo in the opening post.
There are three large wires coming in which I assume are the two lives and neutral. What I assume is neutral goes to a terminal bar with a link to the metal case I understand that this is where you normally make a N-earth link in the US so seems fine to me. However I don't see any seperate ground terminal bar in the picture.
What I don't get is that all of the bare copper conductors which I understood to be ground then connect to what appears to be the neutral bar, while the black and white wires connect to the DP breakers.
Dave I can’t find that thread to look at that panel
[automerge]1568075445[/automerge]
Dave I can’t find that thread to look at that panel
Dave first off that panel looked like crap yes the 3 double pole breakers are using the white wire to carry current and they all needed to be phase taped at least the panel was bonded to the neutral bar the grounding conductor wasn’t phase taped neither, and the cover was off with the main on
[automerge]1568075722[/automerge]
I'm not talking about your previous statement, I'm talking about the photo in the opening post.
There are three large wires coming in which I assume are the two lives and neutral. What I assume is neutral goes to a terminal bar with a link to the metal case I understand that this is where you normally make a N-earth link in the US so seems fine to me. However I don't see any seperate ground terminal bar in the picture.
What I don't get is that all of the bare copper conductors which I understood to be ground then connect to what appears to be the neutral bar, while the black and white wires connect to the DP breakers.
I don’t know what to say but there was a lot mistakes in that panel
[automerge]1568077639[/automerge]
Dave I can’t find that thread to look at that panel
[automerge]1568075445[/automerge]

Dave first off that panel looked like crap yes the 3 double pole breakers are using the white wire to carry current and they all needed to be phase taped at least the panel was bonded to the neutral bar the grounding conductor wasn’t phase taped neither, and the cover was off with the main on
[automerge]1568075722[/automerge]

I don’t know what to say but there was a lot mistakes in that panel
Dave when it comes to multiple conductors in a ( cable ) your allowed to use any color on live except green then again you have to phase tape the wires including white. When it comes to singles up to # 8 the wire has to be the correct color no phase taping. In closing unfortunately the NM cable falls under multiple conductors.
 
Last edited:
Those SQ D Homeline breakers are not UL classified to be used in any competitive panel, and depending on the age is a ITE or Siemens panel, need to be Siemens or UL classified to be used in Siemens panels, breakers that are the same make as the panel are UL listed, but UL does classify some makes to be used in competitive panels, but you need the paperwork to prove it, the only way that should be done in my opinion is when the panel is obsolete & that is the only alternative like FPE, and Zinsco/Sylvania. Siemens is easy to get and just because a breaker fits does does not mean it is OK to use.
 
Those SQ D Homeline breakers are not UL classified to be used in any competitive panel, and depending on the age is a ITE or Siemens panel, need to be Siemens or UL classified to be used in Siemens panels, breakers that are the same make as the panel are UL listed, but UL does classify some makes to be used in competitive panels, but you need the paperwork to prove it, the only way that should be done in my opinion is when the panel is obsolete & that is the only alternative like FPE, and Zinsco/Sylvania. Siemens is easy to get and just because a breaker fits does does not mean it is OK to use.
If you put a breaker in your panel and it’s not the same brand name an inspector will fail that application. It’s like you said these old panels like Westinghouse, federal pacific, etc. Even though the breakers fit an inspector will fail it. It kind of sounds like you need an upgrade to your panel and Siemens makes a good panel
 
If you put a breaker in your panel and it’s not the same brand name an inspector will fail that application. It’s like you said these old panels like Westinghouse, federal pacific, etc. Even though the breakers fit an inspector will fail it. It kind of sounds like you need an upgrade to your panel and Siemens makes a good panel
There is no problem finding the correct breaker for that panel I attached some info to help, always liked ITE breakers and that is what current production Siemens QP, and Murray MP are just different branding. Since Siemens chose to discontinue the ITE brand and understand they are doing the same with Murray, paperwork like the below information makes the inspection process easier.
 

Attachments

  • UL Letter of Authorization to Substitute I-T-E Gould and Siemens Circuit Breakers(1).pdf
    43.6 KB · Views: 0
  • UL breaker-substitutions-murray-MH-T(crouse hinds)1.pdf
    35.1 KB · Views: 0

Reply to 14-50R ground/neutral question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an existing but unused 50A disconnect on the side of the house. It had been connected to an AC unit that got replaced. It has just 3...
Replies
4
Views
954
I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
427
I have breaker box at least 40 yrs old, both conduit and romex enter box, only one neutral bar that all white wires and bare ground wires attach...
Replies
4
Views
764
I'm starting a new construction single-family residence, I know with the 2020 NEC they require an emergency disconnect on the exterior of the...
Replies
5
Views
2K
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
447

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock