I have installed 150mm tri rated cables replacing old existing cables with loose crimps which were over heating.
and identified by a heat mapping report carried out on site.
The runs from the isolator to the contactor within the panel are very short, about 200mm and not straight, hence I have had to put a loop on each one. This was the only way to bring the tails onto the lugs square and straight. The originals were straight but very tight.
Its feeding a large 3 phase motor which sits at around 260 A once up and running. 400A BS88 overcurrent devices.
Connections are all good, just wondering if the single loop/circle Ive made with each tail may cause any problems.
Probably a silly question but thought it worth an ask with such large currents/tails
cheers
 
260 is a baby!

It's no problem, just doesn't always look the part. 150mm is very large for 260A generally.

Tri is rated at 105degC and without looking you could have probably dropped down a couple of sizes.
 
It's all well taking the temperature rating of the tri @ 105 which it is, but, are the connected devices rated @ 105, I doubt it.
They are probably 70 deg C rated, thus, you must size the interconnects for the installed cable size/rating to keep the running temperature down to the limit imposed by the connecting devices.
OP you mention panel, so MCC to EN 60439/61439, or panel under EN 60204?
This may have an affect on the cable rating due to the potential differences in allowable cable ratings for different installations methods experienced in the different standards.
Either way, BS7671 ratings are irrelevant, and the OEM ratings may be more relevant as long as they reflect the as installed state.
 

Reply to 150mm Tri Rated in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi guys I’ve got a motor starter I’ve come across and looking at the electrical drawings it’s originally had 35mm tails from a 100amp fused...
Replies
4
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
173
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
957
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock