I hace been asked to move a CU from next to a 3phase board in a boiler room to an office about 12 m away in the same building. It is a one story building and I am proposing taking the cable through the loft.

I'm not sure if I should use 2 core 25mm SWA or 25mm meter tail cable. The total distance allowing for getting up and down fro mloft will be 15m. I am allowing for a max load of 100amps, though it wont be as high as that.

Any thoughts/ advice appreciated,

Andy
 
My weapon of choice would be:

4175splitconc.jpg
 
Subcategory - 4. Standards Relating to Cables



Having designed the circuits to supply 6 flats contained within a building, They require 25mm supply cables to their respective consumer units. Split Concentric cable to BS 4553-88 is lighter, easier to install and cheaper than SWA. Can I use this cable, with suitable protection to run from the switched fuse at the origin of the supply to the consumer units in the flats

starline.gif


Split Concentric
Previous editions of the Wiring reguations have allowed the use of split concentric cables in concealed walls.
We would however refer you to the current 17th edition of the Wiring Regulations, specifically section 522.6.5 - 522.6.8, with regard to running cables in buildings. It should be noted that split concentric cable does not comply with the requirements of these clauses.


Typed split concentric in google, cos never heard of it before, and this came up, from Voltimum, its a question, and tha answer is from pyrismian cables.

thought you might like to know!
 
Subcategory - 4. Standards Relating to Cables



Having designed the circuits to supply 6 flats contained within a building, They require 25mm supply cables to their respective consumer units. Split Concentric cable to BS 4553-88 is lighter, easier to install and cheaper than SWA. Can I use this cable, with suitable protection to run from the switched fuse at the origin of the supply to the consumer units in the flats

starline.gif


Split Concentric
Previous editions of the Wiring reguations have allowed the use of split concentric cables in concealed walls.
We would however refer you to the current 17th edition of the Wiring Regulations, specifically section 522.6.5 - 522.6.8, with regard to running cables in buildings. It should be noted that split concentric cable does not comply with the requirements of these clauses.


Typed split concentric in google, cos never heard of it before, and this came up, from Voltimum, its a question, and tha answer is from pyrismian cables.

thought you might like to know!

In other words, treat it like T&E.
 

Reply to 15m distirbution circuit - cable choice in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi there. I am a doing some DIY kitchen work. In Ontario Canada, code allows either a split 15 amp multi-wire circuit or a 20 amp circuit (each...
Replies
0
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
548
Hi, I am a mechanical engineer tasked with some electrical engineering scope of work and not sure where to look for information on the...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock