I am in a.bit of a tiz with this one, an external light with no built-in fuse carrier is required to be fed by a 16A socket backed up by a 16A rcbo due to the fact the socket will some time be used to supply a heavier load. What about over current protection of the light.
 
As above, probably what I would do is metal-clad FCU and a couple of plastic glands to grip the cable. Could be switched if you need a operational switch somewhere, otherwise just fuse only.
 
Hi guys.
I am in a.bit of a tiz with this one, an external light with no built-in fuse carrier is required to be fed by a 16A socket backed up by a 16A rcbo due to the fact the socket will some time be used to supply a heavier load. What about over current protection of the light.
As a fixed load it doesn't require overload protection, but does require fault current protection, so providing the cable supplying the light etc is suitable for protection by 16A it is completely acceptable as is....

Unless the luminaire has a note stated "this must be protected by a 6A mcb" or similar, in which case fit a fcu with a 3A fuse between the plug and luminaire.
 
'Fixed load' was being used to mean 'unable to create an overload condition'' rather than 'fixed in position.' A lamp generally cannot cause an overload so as per @Julie. it does not need overload protection. If the lamp were somehow able to draw 3A it would be on fire, so there is no point fusing the 16A supply down to 3A to protect against overload as it won't. Therefore only fault protection would benefit and that is more or less down to the choice of cable unless the MI's state otherwise. Wire it in 1.0 sq, mm and there is no point fusing that down below 16A either.
 

Reply to 16A socket with 3A load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
883
Situation is garden summerhouse fed by own 16A RCBO in consumer unit in garage over 4mm2 (overkill !) SWA . At summerhouse this goes to sockets...
Replies
13
Views
2K
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock