Search the forum,

Discuss 16mm T&E in the UK Electrical Forum area at ElectriciansForums.net

Generally with 16mm t&e a separate 10mm is run for bonding and the CPC of the 16mm T&E is just that..... A circuit protective conductor.

I used a bit of 16mm T&E as a distribution circuit on a new build the other day due to aesthetics. I've had a separate meter box installed to house the switch fuse next to the actual meter box. I've run the cable up the wall internally through joists and down to the consumer unit. I've used a metal capping that the manufacturer states provides adequate protection from nails, screws and the likes of.

Reason I chose to use 16mm T&E over 16mm SWA is the consumer unit is installed on show in a utility room and an SWA glanded in top or bottom would look rubbish IMO.
So what do you do if the consumer unit is shown on plans on a stud or metal stud wall .The reason it was opted as swa was for this reason being c.u hight should be at part m hights (yes I know it is not directly under part M but part P) on a stud wall and this type of capping was not readaly available.
 
So what do you do if the consumer unit is shown on plans on a stud or metal stud wall .The reason it was opted as swa was for this reason being c.u hight should be at part m hights (yes I know it is not directly under part M but part P) on a stud wall and this type of capping was not readaly available.

on a stud wall(metal or wood) use metal copex and slap a bonding clamp just behind the fuseboard....
 
So what do you do if the consumer unit is shown on plans on a stud or metal stud wall .The reason it was opted as swa was for this reason being c.u hight should be at part m hights (yes I know it is not directly under part M but part P) on a stud wall and this type of capping was not readaly available.

If the stud wall is made of metal then you've got to satisfy the requirements of 522.6.203. IMO the easiest option would be then to use SWA. If the stud wall is made of wood and you can install the cable deeper than 50mm (if stud wall is thicker than 100mm to the revearse side) then T&E can be used without any additional protection. If you can't achieve a depth of more than 50mm then you've got to meet the requirements of 522.6.203 (i) or 522.6.204 and 522.6.202 .
 
New houses have sub-dist circuits wired like this for years.

I suppose that would depend on the calculated or selected csa of the protective conductor. Although I note 543.2.1 says a protective conductor may consist of one or more of the following.....

Might be just one of those 'good or poor practise' myths, then?
 
If the stud wall is made of metal then you've got to satisfy the requirements of 522.6.203. IMO the easiest option would be then to use SWA. If the stud wall is made of wood and you can install the cable deeper than 50mm (if stud wall is thicker than 100mm to the revearse side) then T&E can be used without any additional protection. If you can't achieve a depth of more than 50mm then you've got to meet the requirements of 522.6.203 (i) or 522.6.204 and 522.6.202 .

Lee how would you feel about using swa and not mechanically terminating it into the db but float it into the back when coming down a stud wall, glanded at supply end and bangod at supply end? Not best practice maybe but i do like swa used in such instances rather than pvc 16mm t&e & tails.
 
As an aside, I note that 16mm 6242y cable only has a ccc of 85amp only when clipped direct 'C' (Table 4D5).

Just wonder how that method is achieved in a modern built house? Not suggestion incorrect installation here, but for another thread I found the IET suggested installation above a ceiling was method A, so I thought in an in-insulated stud wall would be similar?
 
Generally with 16mm t&e a separate 10mm is run for bonding and the CPC of the 16mm T&E is just that..... A circuit protective conductor.

I used a bit of 16mm T&E as a distribution circuit on a new build the other day due to aesthetics. I've had a separate meter box installed to house the switch fuse next to the actual meter box. I've run the cable up the wall internally through joists and down to the consumer unit. I've used a metal capping that the manufacturer states provides adequate protection from nails, screws and the likes of.

Reason I chose to use 16mm T&E over 16mm SWA is the consumer unit is installed on show in a utility room and an SWA glanded in top or bottom would look rubbish IMO.

Any links to this metal capping Lee? Would it stop an sds drill in your opinion?

I generally prefer to use SWA, especially as the CCC is greater too. In your situation I have installed a galv adaptable box at first fix stage, fixed at a suitable depth into the wall so its roughly flush with the finished plaster surface. With the SWA glanded into this, at second fix all you have to do is take the lid off and screw the CU over the top.
 
Any links to this metal capping Lee? Would it stop an sds drill in your opinion?

I generally prefer to use SWA, especially as the CCC is greater too. In your situation I have installed a galv adaptable box at first fix stage, fixed at a suitable depth into the wall so its roughly flush with the finished plaster surface. With the SWA glanded into this, at second fix all you have to do is take the lid off and screw the CU over the top.

Just had full rewire done, cables very close to surface or coming through skim - http://www.electriciansforums.co.uk/threads/just-had-full-rewire-done-cables-very-close-to-surface-or-coming-through-skim.117855/page-4#post-1235074
 
Any links to this metal capping Lee? Would it stop an sds drill in your opinion?

I generally prefer to use SWA, especially as the CCC is greater too. In your situation I have installed a galv adaptable box at first fix stage, fixed at a suitable depth into the wall so its roughly flush with the finished plaster surface. With the SWA glanded into this, at second fix all you have to do is take the lid off and screw the CU over the top.
This is how we used to do it as I said in post before the capping was not readly available ( off shelf) at wholesalers
 

Reply to 16mm T&E in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock