Would a 16th edition board class as a fail on a perioic,all socket circuits on rcd side and
all lights on non rcd side,as the customer does not want a new board installing.
 
Would a 16th edition board class as a fail on a perioic,all socket circuits on rcd side and
all lights on non rcd side,as the customer does not want a new board installing.

NO. If it was compliant when it was fitted then it is OK now, the wiring regs are not retrospective. So you need to make no comments if all tests and insp's are OK
 
Non RCD protection of cables in walls less than 50mm etc would only warrant a code 4 on a PIR. When it was installed it complied with the regs (16th), now it just doesn't comply with the 17th doesn't mean it's dangerous, hence a code 4.
 
Yep I'm going code four. Also, if there is no RCD on lighting, is there sufficient supplimentary bonding in bathroom etc?
 

Reply to 16th edition board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock