Search the forum,

Discuss 1970's Wiring Modification and My Liabilities? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
Helpful and constructive advice only please. I appreciate this inquiry isn't ideal.

As a mainly petrochemical Sparky I've been asked to help a mate out re-do a 1970's kitchen. I would love to avoid this job like the plague as, as ever it's all being done on a budget and as minimal hassle as possible but he's a good mate asking. The customer wants the kitchen re-wired. There's no main water bond, or gas and being a terrace it's not going to be possible to put one in without ripping upstairs apart. Solid floors/flat roofs also hinder this. The current C.U. is a wooden backed 4 way fused Wylex with just one ring main and no additional RCD unit has been installed. I've made my opinions of this arrangement clear to the customer :behead:.

I really do not want to have anything to do with the current wiring by adding my new kitchen circuit to the existing ring as such. In a bid to isolate my new work and therefore liability from this current 1970's TN-C T&E PVC installation is there any reason why I couldn't add an RCD protected garage unit to the kitchen, (changing the main C.U. is off limits) fed off the existing ring main (continuity tested) then run my kitchen electrics off this and if necessary bond the water to my garage board earth bus-bar or use a TT stake? Am I wholly responsible for installing the main bonding? I've made it clear to the customer if she wishes to have the work certified she will have to contact the Building Control Dept. as I refuse to join the NICEIC, etc as this is not my field. I feel she won't worry herself too much with this but as the home-owner under Part P this is upto her.

Many Thanks for your constructive thoughts.
 
I am afraid what you are proposing is wholly inappropriate for a competent install. You cannot fit a consumer unit to a ring final circuit and you are not permitted by the wiring regulations to omit upgrading the earthing and bonding if required.
I am assuming, in relation to Marvo's post above, that you mean TNCS earthing.
If so then this makes the bonding requirements even more onerous and bonding to a ring final circuit cpc is not suitable.
If you were just extending existing circuits and not creating new ones for the kitchen then this would not require notification to building control.
Obviously the BS7671 certification would still be required.

I would suggest that you do not get involved with this job as the customer is not prepared to have the required protections in place, even if it is a mate, I would leave this to someone else.
 
In the same way that the customer won't be keeping their old kitchen counter top because it won't fit, you cannot keep the same old electrics. Simple as. Any good mate will respect you for saying so, good advice costs nothing.
 
As above comments!! No-one can convince me that spending 50 quid at BQ on a new fully loaded 17th ed consumer unit is ''off limits'', if it is then as others say, ....walk away!! As for the bonding, i'd rather connect to the water/gas pipes anywhere convenient, rather than leave them unbonded....
 
Thanks for the thoughts.
With this and the other replies in my artillery I was able to get a significantly higher budget to work with and am happier about getting involved. I hate appearing to be "making more work" for myself but think the customer is happy all my recommendations are necessary.
I would appreciate more thoughts on where the law and the regulations cross over. Obviously BS7671 is a British Standard, not law. The 17th edition as I understand it states any new CU fitted should be a split load jobby. I definitely do not have room for even a small one inside the cupboard. Is there any problem with fitting a 16th edition C.U?
As for me suggesting she contract Build Control that was purely for the certification as I am not NICEIC registered so cannot issue a MWC myself.

Cheers.
 
Agreed it might cost us £50 to buy it but with my costs of going out to get it and then my time spent taking the old one out and installing the new one in a very awkward space soon costs a lot more :( Plus it's not just the C.U. if I were to take the job on she'd have proper earthing and a new ring main to add to the bill. Got the feeling she "just wanted some sockets moved", easier said then done :-o
 
Rough price for a kitchen refit and new CU = £1000

Enough said.

Thanks Murdoch. I advised the kitchen fitter who got me the job I wouldn't expect much change from £800. As there's no cooker or lighting circuits to worry about. Just a new ring main, two 10mm earths and small C.U. He told the customer put £1000 aside if you want me to do it so you're bang on Cheers.
 
Thanks Murdoch. I advised the kitchen fitter who got me the job I wouldn't expect much change from £800. As there's no cooker or lighting circuits to worry about. Just a new ring main, two 10mm earths and small C.U. He told the customer put £1000 aside if you want me to do it so you're bang on Cheers.

Plus LABC fees - so that's another £350 round my way.


Whats a ring main?
 
im gonna megger this here ring main I just wired for the kitchen.

why do you guys moan about rfc anf ringmain but not ir tester and megger?

impossible for me to megger any circuits as firm doesnt own a megger

LOL, definitely feeling this Shanky. Never got the whole RFC thingy. Bulb Vs Lamp, I'm with the majority on but I'm afraid it was always a ring circuit and to a lesser degree a Megger during my college/apprenticeship.

The £350 is surprising for the LABC fee's but that's not part of my quote fortunately. Up to the customer if she wants to pay that when I've gone/during the works O:)
 
Last edited:
LOL, definitely feeling this Shanky. Never got the whole RFC thingy. Bulb Vs Lamp, I'm with the majority on but I'm afraid it was also a ring circuit and to a lesser degree a Megger during my college/apprenticeship.

The £350 is surprising for the LABC fee's but that's not part of my quote fortunately. Up to the customer if she wants to pay that when I've gone/during the works O:)

May not be part of your quote matey, but your responsibility to tell the customer they need to do it!
 
May not be part of your quote matey, but your responsibility to tell the customer they need to do it!

I certainly will, all my communications have a footer that clearly states to all my customers that albeit I'm qualified and working to 17th edition any Part P/MW need certifying and the two options they have are to use a registered Spark or contact LABC and as the Homeowner the onus is upon them.

Cheers.
 
Thanks for the thoughts.
With this and the other replies in my artillery I was able to get a significantly higher budget to work with and am happier about getting involved. I hate appearing to be "making more work" for myself but think the customer is happy all my recommendations are necessary.
I would appreciate more thoughts on where the law and the regulations cross over. Obviously BS7671 is a British Standard, not law. The 17th edition as I understand it states any new CU fitted should be a split load jobby. I definitely do not have room for even a small one inside the cupboard. Is there any problem with fitting a 16th edition C.U?
As for me suggesting she contract Build Control that was purely for the certification as I am not NICEIC registered so cannot issue a MWC myself.

Cheers.

BS7671 does not require split RCD boards, it requires that circuits and protective devices be arranged such that danger/disruption/inconvenience or whatever in the event of a device tripping is kept to a minimum.

You can interpret this however you wish. A lot of people read it as allowing half of the installation to go off if a fault occurs, so if an immersion heater was to go faulty it's perfectly acceptable for all of the downstairs lights to go off for example.
Personally I interpret it as requiring circuits to be protected individually and so use double pole RCBOs for domestic boards.
 
The way to go here is to install a 6 way CU with RCBO's protecting the existing 4 circuits and any circuit(s) that you install. The main bonding of the water/gas services will need to be addressed whatever you decide to do.... Personally i would not use a garage unit just to supply the kitchen sockets leaving the rest of the installation WITHOUT any form of RCD protection. If your going to do the job properly then, do it right and change out the existing course protection BS3036 Wylex CU for an RCD/RCBO protected CU!!
 

Reply to 1970's Wiring Modification and My Liabilities? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top