I am not sure if this is acceptable?

If I am using a 2 module enclosure for 2 MCBs both fed from a MCB in the main consumer unit. Would I have to use a busbar inside the 2 module enclosure or would it be ok to have a cable link at the bottom of the MCBs.

I have heard people say this is a nono inside a C/U, but my thinking in this example is that as long as the cable is rated high enough for the MCB from to C/U then there shouldn't be a problem as overcurrent protection is provided by the MCB feeding the 2 MCBs

Thanks Marcus
 
you should have a D/P switch in that unit in order to isolate. therforei suggest you buy one of these. I f fed from RCD on main CU, replace the sub . RCD witha D/P switch.

https://www.NoLinkingToThis/p/british-general-5-module-3-way-populated-garage-consumer-unit/1926g

do it right
 
you should have a D/P switch in that unit in order to isolate. therforei suggest you buy one of these. I f fed from RCD on main CU, replace the sub . RCD witha D/P switch.

https://www.NoLinkingToThis/p/british-general-5-module-3-way-populated-garage-consumer-unit/1926g

do it right

ah ok, so there is a requirement for double pole isolation, cool thanks
 
So if it was a metal 2 module enclosure (like the wylex one available at Screwfix) and it was earthed is that then not alright.
What is wrong with that? It should be earthed one way or another, either earth rod if TT or from the feed supply.

not sure there will be space for one of the BG garage c/u
How small is the garage?!

There will always be wall space, unless it is a doll's house!
 
So what is it for? Not enough slots in the CU?!

He has some underfloor heating in the kitchen of a kitchen-dinner, on its own B6 MCB he has added underfloor heating to the dinner part but its total load is just over 1500w so to much to add onto the B6 MCB. The cable for the kitchen underfloor heating is already in and very difficult to replace it is only 0.75 T&E so cant just swap the B6 MCB for a higher rating.

The consumer unit is full up, So a suggestion I said which might work, without ripping all of the plaster down. Was to swap the B6 for a B10 or B16 and then but an enclosure next to the C/U feed from the new MCB via new cable, then a B6 in the enclosure would protect the kitchen floor cable and a B10 for the dinner underfloor heating, on a thicker cable
 

Reply to 2 module enclosure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
309
Hi, I've done some work in a house, I used an existing 10mm cable on a B40 MCB to supply a 2 way consumer unit to control a heat pump and...
Replies
1
Views
1K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
htps://we.tl/t-JHXw09romZ quick share to photo Hi there. I am trying to convert previous cable network cat5e installed when had non fibre in 2015...
Replies
2
Views
938
Guys Need some advice please. I was asked last week to investigate a burning smell in a toilet turned out it was an extract fan one of 2 The...
Replies
3
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock