Discuss 2 phase dc to ac converter in a 3 phase house in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

S

savimagc

I am about to buy a Pv Solar system for my house(Grid tied system ), the system is a 10Kwatt system, the company that is going to install it, is quoting me a 2 phase DC converter but my house has a 3 phase transformer, they said that there is no problem, but i am not so sure, any help will we appreciated.
 
not balancing the system properly across the 3 phases is bad practice, and pretty daft as 3 phase inverters cost no more than 2 phase.

Definitely get a second quote and see what they say - from a company that knows what they're doing preferably.
 
i agree about about getting a 3 phase inverter. but correct me if i am wrong, but as its a pv system its a negative load so in theory will not be creating an imbalance across the phases.
 
i agree about about getting a 3 phase inverter. but correct me if i am wrong, but as its a pv system its a negative load so in theory will not be creating an imbalance across the phases.
of course it will. Think how balance works, it has just the same impact either way round, actually it could have more impact if it involved 1 phase exporting backwards through the transformer while other phases were importing.
 
of course it will. Think how balance works, it has just the same impact either way round, actually it could have more impact if it involved 1 phase exporting backwards through the transformer while other phases were importing.

didn't think of that, I've never really thought about it as I would always use a 3-phase inverter in this situation.
 

Reply to 2 phase dc to ac converter in a 3 phase house in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello right off the bat I'm a novice with a little better understanding than most(father was a electrician) but I am not an electrician. I'm...
Replies
26
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
284
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
600
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
656
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock