Discuss 2 phases into standard CU? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

hagmeister

I want to introduce an IR heating system into an existing split load CU. It is supplied at the moment by 1 phase of a 3 phase input, controlled by a 60A main fuse and a 40A meter. The 5 existing circuits are 2 x 32A ring mains, 2 x 6A lighting and 1 x 16A water heater.
The total wattage for the heaters would be 9KW, giving a potential draw of 39.13 amps.
Is it ok if I move the 5 existing circuits to the dipole (mains) side of the split, (with rcbo protection) and route the new heating circuits thru 32A and 16A MCB's (2 heaters and 1 heater) using another rcbo as a dipole on the other side of the split, using a second phase and another 60A mains fuse + a new meter? I know I would have to clearly label the new RCBO as MAINS or should I add another mains dipole and rcbo from the second phase and meter?
Or would this be totally out of the question as there would now be 2 x 230v supplies entering 1 x 230v CU, even though it is split load? All tails - 25mm2, meters 60/80 amps, earths 10mm2, FUSES 60A and mains feed 40/50mm2 SWA.
Diversity is not easy to calculate for upgrading to 100A with 25mm2 tails and the premesis would be perceived to be commercial.
Thanks for your help - had a few confilcting bits of advice on this...as you can imagine
 
Can you draw and post your idea, i got confused with the amount of info your trying to fit in and your explanation, but what i can make out its not a problem having 3phase within a board but the way your trying to achieve don't sound right, i would just buy a 3phase D.B. change existing meter to polyphase meter and then balance all loads over the phase, a electrical inspection of existing electrics will need to be carried out to make sure you dont create any problems if putting existing across different phasing (borrowed neutrals, proximity 400v labels etc ).

Regarding the main switch and fuse are you refering to the DNO service meter and cutout or is this a consumer property 40amp fuse and meter.... if DNO then you have no authority to interfere with said equipment, can you clarify your experience etc so we can tailor our answers to suit.
 
Last edited:
Off the top of my head I would say no, you would need a 3ph CU. or 2 CU's
Equipment not suitable / designed for the job, their is a reg for this, someone will know the number i am sure.

Hope this helps
 
Just on a safety point, use two CU’s. Clearly mark them as 400V potential between them. I’ve fallen foul of three phase in what looked like a single phase board. Going back many years to 230V three phase under M&Q regs they were confusing to say the least. It would be quite normal the find a single phase board with the bus-bar chopped in to three sections.

Play it safe, don’t be sorry at a later date.
 

Reply to 2 phases into standard CU? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
912
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
657
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
977
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
556

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock