Discuss 2 pumps on one system in the Central Heating Systems area at ElectriciansForums.net

Reaction score
0
Hi there, the heating system I am working on has 6 zones and valves for each zone which was working fine with one boiler and one pump. some rads weren't getting hot so the plumber has installed 2 x pumps, one for 3 zones and another for 3 zones, the problem is I originally had all the oranges from the valves connected to the switch live to boiler and the pump. obviously now I need to somehow split the oranges to feed the appropriate pumps while keeping the single switch live to the boiler from both. I presume I need a relay for this but I have no experience with relays and am stuck as to how to wire them. I have an imo RL01C 8 pin 2 c/o relay but don't know how to wire it.
any help greatly appreciated
 
You will need 2x 8 pin relays, one for each pump.

For each set of 3 valves:
Connect the coil to the orange of the relevant valves.
Connect a permanent live to both commons.
Connect the pump to one of the N/O contacts.
The other N/O contact will be your switched live to the boiler.
 

Reply to 2 pumps on one system in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Up until now I have steered clear of heating systems. I now have quite a bit of work with a builder and will be expected to deal with the...
Replies
4
Views
829
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
932
For the past few years, I have used a hydronic system (outdoor wood boiler) with both high and low temp working simultaneously. The low temp...
Replies
6
Views
760
Friend asked me to wire in a hive on a conventional 1 zone heating system. So I fitted it tested the HIVE and all was working. I then said to him...
Replies
5
Views
862
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
655

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock