Discuss 2 Radials into a 32A B type breaker and other wonders !!! in the Australia area at ElectriciansForums.net

S

Sav

Hi all,
Hope you guys are all enjoying the nice weather and not working inside some dark small cupboard like I was today !!!!
Anyway, here is the scenario. Neighbour comes over this morning and says her fuse for downstairs has tripped and cannot be re-set.
I go and take a quick look and test and found the following.

The downstairs mcb, B Type 32A BSEN60898 Hager controls the living room, the conservatory, the dining room and the kitchen.

I was getting wierd readings, so i took off the sockets and found that the conservatory sockets had live-neutral reversed, the kitchen sockets were not in the ring, but somehow spured off from a junction box which cannot be traced ( under tiled floor or in wall somewhere) and also 2 LIVE AND EXPOSED cables behind the washing machine, just hanging there !! (Old red/black).

I rectified the conservatory sockets and made safe the hanging ones and also traced a faulty leg to one of the kitchen sockets (which had an earth fault).

So now, we have 2 legs in a 32A breaker but not in a ring. As a precaution, i replaced the 32A with a 16A and put both legs into there. The board is a Hager non RCD with 8 ways and no spare ways to separate the legs. is this ok for now, with regards to the 16A mcb, as there is no spare way ( I have advised her that the board is too small for the circuits). The board also has a couple of the lighting circuits doubled up in a 6a mcb and the upstairs ring mcb also a 32A, has a another 2.5mm inside it for the garage supply. I removed this as a precaution.

Best of all, the conservatory was built 3 years ago (by our eastern european friends) and the consumer unit and wiring added then (not a dual RCD board or any RCD protection at all)!!!! The lady says that the sockets were working ok in the conservatory (computer, floorlamp etc ). Please explain !!
Thanks and best regards,
Sav
 
I guess you mean explain why the things worked with the polarity reversed.

Lamps will work ok as they are not sensitive to polarity. Computer probably worked because one of the first things to happen in a computer is to convert the 230V to lower voltages like 12V (usually dc) and this would be done via a transformer, again polarity insensitive.

Not a new theme to your story though! Not the first and certainly not the last!
 
as long as the extra 2.5 coming from the upstairs ring mcb goes to only one socket in the garage or a spur then more sockets, that can go back in the breaker as it is just like spuring off a socket
 

Reply to 2 Radials into a 32A B type breaker and other wonders !!! in the Australia area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
177
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
648
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
736
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
236
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock