I cut one of the cables on my ring circuit, attached the 2 now separate ends to a new 30a junction box, and then run 2 additional spurs from the same junction box, using 32a twin and earth, on the end of each of these new spurs is a twin plug socket with usb.

I did the work with my father in law, who’s an avid DIYer and has been doing diy for 60 years.

We did a really good job, cables cut nice, neat, secure, tested them, and all working.

Due to a rush to get the job done before decorators, I pre installed the new sockets and cabling, ready for the junction, and only then did I realise I should have extended the ring.....it was too late, I had sealed the walls up and could not get another cable in. We used a square 30a MK box, which had ample room for the cables.

These are bedside outlets, not for heavy consuming items.

Some forums and people have now put the fear of god in me that this is dangerous, however I have read mixed opinions (e.g. apparatly 1 spur from any point is the Reg, ok.....so I have 2 on mine, but is this really much different than if I added another junction 10 inches away for my second spur)

Is this really a concern to warrant me ripping it all back out?

It’s a good tidy job.
I know there’s regulations and partP......hindsight is a wonderful thing.

Views?
Many thanks.

452805D2-13E6-4F2C-A5C7-A949BBC783E1.jpeg
 
where does it say there may be other means of meeting 433.1?
It doesn't have to say that specifically, you just have to meet it. Just because they gave a few options for free doesn't mean that's exhaustive. If you follow the guidance, you will definitely meet the regs, if not, you have to decide for yourself.
This is a very common pattern also used in all parts of the building regulations nowadays. The building regs just say something very hard to use, and the Approved Documents give specific examples that should cover most situations.
 
It doesn't say you shouldn't wire a banana form a junction box to a tomatoe in a ring final, dies that mean you can.
actually it specifically states they have to be copper conductors :p

but more generally, the regs are generally pretty clear about what standards cable, accessories and junction boxes must conform you.
 
It doesn't have to say that specifically, you just have to meet it. Just because they gave a few options for free doesn't mean that's exhaustive. If you follow the guidance, you will definitely meet the regs, if not, you have to decide for yourself.
This is a very common pattern also used in all parts of the building regulations nowadays. The building regs just say something very hard to use, and the Approved Documents give specific examples that should cover most situations.
Fair enough I’d be inclined to follow the regs though that way if you ever did end up on the chopping block you just point out the note at the front of the regs about complying with EAWR
 
Let me ask the question in another way...

You've just been asked to inspect the OPs property for an EICR and you find this junction box, it's been changed to a maintenance free one so that's no longer an issue.

How would you code the fact there are two spurs taken from the one junction box and what regulation would you quote to substantiate that coding?
C3 not to current standards citing reg 433.1 and mention Appx 15.
I think the wording is quite clear in saying that Appx15 is showing the design options. As in the options on how to spur from a ring rather than the diagram being one of many different options.

Out of interest how would you justify not coding it?
 
Last edited:
C3 not to current standards
c3 is actually "improvement recommended" (as it would improve the safety of the installation) According to Electrical Safety Council’s Best Practice Guide 4,
upload_2018-10-22_23-27-43.png

So in fact, even if it were non compliant, it shouldn't be the subject of a classification code unless it affects the safety of the installation.
 
c3 is actually "improvement recommended" (as it would improve the safety of the installation) According to Electrical Safety Council’s Best Practice Guide 4,
View attachment 45070
So in fact, even if it were non compliant, it shouldn't be the subject of a classification code unless it affects the safety of the installation.
Nice catch :thumbsup: id still C3 it because it could affect the safety of an installation there may even be an argument for a C2 because it could be potentially dangerous,in the event of an overload
 
Very rare I disagree with your stance on electrics but I think your enterpretation based on if it doesn't say you can't do something in the regs then you can do it.

It doesn't say you shouldn't wire a banana form a junction box to a tomatoe in a ring final, dies that mean you can.

433.1 says what you can do.

Thank you for those kind words.

I think my hard line stance makes it come across that way, but that's not really what I'm getting at.

In the course of this thread, I've read 433.1 several times and it makes no mention of junction boxes. It's focus is on cable loadings and ensuring that they are adequately protected against overload through the correct selection of cable size and appropriate OCPD.

Specifically 433.1.204 states the rules for cable sizing for ring finals.

Since these two spurs are designed correctly, i.e. the correct size cable and only one double socket outlet on the end of each, the spurs themselves comply. The ring final itself complies because it is wired in an appropriate cable and protected by an appropriate OCPD.

So the three elements here comply in their own right. Providing the junction box used can handle the expected load (whether or not this is accessible is another discussion), there is no reason that I can see how this arrangement can be deemed to be a non-compliance.

The appendix 15 argument if taken to it's logical conclusion means you can never have a single socket outlet on a ring final, or take a spur from the origin, or have more than two double socket outlets after a fused spur, or have a grid switch system... why? Because they aren't shown on the diagram. The diagram provide guidance on how to comply, it's not a definitive list of what you can do (as it states, the diagram shows options).

And part of why I'm taking a somewhat hard line stance is because I'd like to see more substantiated 'it's against regs'. If I make statements to that effect I try and provide appropriate regulation numbers as it may help someone understand more. And in this case, no body has been able to explain to me how this arrangement doesn't comply without resorting to the appendix 15 argument.
 
C3 not to current standards citing reg 433.1 and mention Appx 15.
I think the wording is quite clear in saying that Appx15 is showing the design options. As in the options on how to spur from a ring rather than the diagram being one of many different options.

Out of interest how would you justify not coding it?

At the moment, I couldn't justify a code because I genuinely do not believe it contravenes any of the regulations in 433.1. Hence why I'm asking which regulation it contravenes and why.

I would possibly inspect it and look for signs of thermal damage to the junction box and the cabling that may suggest an overload situation, but the arrangement itself whilst a little unorthodox doesn't appear to breach 433.1 for the reasons I've outlined above.
 
id still C3 it because it could affect the safety of an installation there may even be an argument for a C2 because it could be potentially dangerous,in the event of an overload

Nooooo! Not the overload argument again!

There is no more risk of overload with what the OP has done, than with two spurs taken from different points on the ring. Subject to the junction box making a sound connection, which is a caveat we've been accepting all along.

I will state categorically that this method is just as safe as any other. The only debate is about whether it technically complies as a configuration, which I think it does.
 
Thank you for those kind words.

I think my hard line stance makes it come across that way, but that's not really what I'm getting at.

In the course of this thread, I've read 433.1 several times and it makes no mention of junction boxes. It's focus is on cable loadings and ensuring that they are adequately protected against overload through the correct selection of cable size and appropriate OCPD.

Specifically 433.1.204 states the rules for cable sizing for ring finals.

Since these two spurs are designed correctly, i.e. the correct size cable and only one double socket outlet on the end of each, the spurs themselves comply. The ring final itself complies because it is wired in an appropriate cable and protected by an appropriate OCPD.

So the three elements here comply in their own right. Providing the junction box used can handle the expected load (whether or not this is accessible is another discussion), there is no reason that I can see how this arrangement can be deemed to be a non-compliance.

The appendix 15 argument if taken to it's logical conclusion means you can never have a single socket outlet on a ring final, or take a spur from the origin, or have more than two double socket outlets after a fused spur, or have a grid switch system... why? Because they aren't shown on the diagram. The diagram provide guidance on how to comply, it's not a definitive list of what you can do (as it states, the diagram shows options).

And part of why I'm taking a somewhat hard line stance is because I'd like to see more substantiated 'it's against regs'. If I make statements to that effect I try and provide appropriate regulation numbers as it may help someone understand more. And in this case, no body has been able to explain to me how this arrangement doesn't comply without resorting to the appendix 15 argument.
In that case it may well be technically compliant because there isn’t a reg forbidding it so it’s wrong because it just is :p good point about the grid switches etc hadn’t thought of that.
Nooooo! Not the overload argument again!

There is no more risk of overload with what the OP has done, than with two spurs taken from different points on the ring. Subject to the junction box making a sound connection, which is a caveat we've been accepting all along.

I will state categorically that this method is just as safe as any other. The only debate is about whether it technically complies as a configuration, which I think it does.
I was thinking more overloading the actual junction box itself rather than the wiring... but I do see your point potentially anything could be plugged into any socket and cause an overload anywhere
 
Last edited:
The current through the junction box will be no higher than it might be in other applications on a ring. E.g. taking one spur from a point near the CU. The question is whether it makes a sound connection to four cables. If it does not, then it is non-compliant like any accessory that does not make a sound connection.
 
Ok, but where in 433.1 does it preclude taking two spurs from a single point on a ring final circuit?

That's all I'm asking.

I can't find a regulation that precludes it, but I'm happy to be proved wrong because then I'll have learned something new :)

I'm thinking the same thing. As the OP passed the ring through the JB, then this is 2 separate spurs in a single junction box, not a single spur with 2 twin sockets attached to it.

Both sockets are in effect independently spurred from the RFC by nature of the fact that both are independently connected to it. You could remove either socket and the other would remain connected. So... does that not qualify as 2 spurs, one for each socket?

What is the difference between breaking into the RFC twice in one JB, or once in each of two JBs next to one another? Do the regs say two spurs can't connect back to the RFC within a single enclosure?

At very least, it's not dangerous in anyway that I can see - other than a none MF box technically in an inaccessible location, but that's very easy to remedy.
 
Let me ask the question in another way...

You've just been asked to inspect the OPs property for an EICR and you find this junction box, it's been changed to a maintenance free one so that's no longer an issue.

How would you code the fact there are two spurs taken from the one junction box and what regulation would you quote to substantiate that coding?

I feel like an apprentice again, or worse a Electrical Trainee.

I’d grade it with a squiggle that cant be deciphered - I’ll make it look like a 1,2,3 and a tick, maybe even a N/A to cover all basis.

I’m off to bed. If I dream about spurs, I hate you all.
 
I feel like an apprentice again, or worse a Electrical Trainee.

I’d grade it with a squiggle that cant be deciphered - I’ll make it look like a 1,2,3 and a tick, maybe even a N/A to cover all basis.

I’m off to bed. If I dream about spurs, I hate you all.
Bet you will as well :rolleyes: sockets and JBs and wagos as you to ss and turn
 
I have watched and read...some very erudite prose on this thread, and that's why I am here...learning every day.
The juxtaposition bewtween regs and practicality, recommendations and actuality, all fascinating for me!
At the end of the day, common sense seems to say that it's 2 spurs, each one ok provided the termination is good, just a question over whether the hardware selected is appropriate...
Sparkychick, like your clarity on this.
 
Don't think so, sparkychick...nice clean JB connections, 2 spurs, leccy good at each one...overload?
where couldn't you, on any circuit not fused down?
Right, really going now!
 
I think that’s the wonderful thing about the regs. They are open to interpretation so we are probably all wrong it’s really only down to yourself and how you justify it that makes it right or wrong everything is right if you can justify it.

Yeah, but that's also what makes it somewhat scary :)
 
Yeah, but that's also what makes it somewhat scary :)
Yup it would be much better if it was all black and white but it’s grey so the people that wrote it can weasel out throw you under the bus and say thats not how we meant it if you follow it and end up burning down a house killing a family of 5 sheep and destroying a museum.
 
Yup it would be much better if it was all black and white but it’s grey so the people that wrote it can weasel out and say thats not how we meant it if you follow it and end up burning down a house killing a family of 5 sheep and destroying a museum.

As @Murdoch said earlier, I wish they'd focus on clarity instead of climbing into bed with the manufacturers to push their fancy (read expensive) new safety devices.
 
As @Murdoch said earlier, I wish they'd focus on clarity instead of climbing into bed with the manufacturers to push their fancy (read expensive) new safety devices.
That would be epic but there is a probably another hidden agenda as well they know exactly what they want to say but it will take another 24 editions and multiple amendments for it to be clear - the IET is a very profitable business indeed
 
That would be epic but there is a probably another hidden agenda as well they know exactly what they want to say but it will take another 24 editions and multiple amendments for it to be clear - the IET is a very profitable business indeed

So maybe the end of next year then we might get some clarity? ;) Either that or we'll all be broke and out of business :D
 
It's still on my mind too and I'm in bed now!!

I'm resolved though, it IS two spurs, it just is. Certainly in every way that matters, it is 2 spurs.

The regs don't cover this. They go far enough to limit overloading of a single spur, they don't cover the possibility of putting 2 in one box because you just don't need specific regulation for that.

As for is it right or wrong to do it this way... If it's not dangerous and doesn't explicitly break regs then it's not wrong. All we have here is something a little unusual. But hey, saved on a second jb and shortened the install time too.

Just a shame an mf box wasn't used for the sake of compliance, but that's a different topic really. And a topic I have some divisive views on so maybe another thread for that tomorrow night :)
 
It's still on my mind too and I'm in bed now!!

I'm resolved though, it IS two spurs, it just is. Certainly in every way that matters, it is 2 spurs.

The regs don't cover this. They go far enough to limit overloading of a single spur, they don't cover the possibility of putting 2 in one box because you just don't need specific regulation for that.

As for is it right or wrong to do it this way... If it's not dangerous and doesn't explicitly break regs then it's not wrong. All we have here is something a little unusual. But hey, saved on a second jb and shortened the install time too.

Just a shame an mf box wasn't used for the sake of compliance, but that's a different topic really. And a topic I have some divisive views on so maybe another thread for that tomorrow night :)

and it uses a screw type JB in an inaccessible location .....:):)
 
all depends on how you define "inaccessible".if a screw type JB is installed under a screwed down floorboard trap, it's accessible by the use of a screwdriver: same as the screw terminals in a CU are accessible by the use of a screwdriver. now where's my tin hat?
upload_2018-10-23_8-13-51.jpeg
 
and it uses a screw type JB in an inaccessible location .....:):)

It's a nonsense imo. Make it as accessible as you want and no one will inspect/maintain it until there is a fault someday. And does a correctly torqued screw terminal work free over time? In theory it can... But in reality I find it not to be the case.

We have a number or mobile machines here with 63a 3ph plugs on a trailing lead. As such, at least once a year as part of testing the plugs are opened and the terminals checked - and they're never loose! Not even fractionally. Sure, it helps that they use screw clamp terminals but on the other hand a plug on a trailing lead is in theory an item most exposed to movement of the cable entering it.

I also see others using a drop of threadlock on the terminal screws to prevent and future movement.

The OPs installation doesn't qualify as 'accesible' I know. But it emphatically is accessible by anyone with the ability and tools to open the JB to inspect it, as the only barrier to access is a floorboard fixed with 2 screws - it's as accessible as the JB cover is removable.

The regs say mf under floorboards etc as it's easier to have a blanket rule for all of course. Doesn't do much to encourage common sense thinking though. I personally think the whole MF thing is unnecessary in many such cases and that a good installer can achieve the same long term performance with a screw terminal in anycase.

Let the debate rage ;)
 
I can't speak for @Murdoch but I believe our views on this are pretty similar... it's less about how easy it is to access (at the moment it's easy because there are no fitted carpets), it's more about knowing it's there.

My mantra on the subject is if you can't see it easily when the job is done, make it maintenance free. It saves all the arguments, all the potential issues around subsequent inspection.

That's my personal view, it complies with the regs and no one is likely to change my mind on that :)
 
The OPs installation doesn't qualify as 'accessible' I know.

But it emphatically is accessible by anyone with the ability and tools to open the JB to inspect it, as the only barrier to access is a floorboard fixed with 2 screws - it's as accessible as the JB cover is removable.

which renders it inaccessible - are you suggesting that we need to be prepared to lift ALL floorboards to inspect whats hidden - no

There is a reg that says something about items being accessible and under floor boards ISN'T
 

Reply to 2 spurs from a Junction Box....worried? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock