Discuss Spur of midpoint of ring? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket?

Mate of mine wanted me to see if "a couple of wires were dead". Looks like old ring main, but they go in the wylex fusebox, so will have to check they are properly removed. Ends tapped up. His ceiling is like a series of mini-strokes. There is some kinda other ring or two in the ceiling but with lots of brown connection boxes. Just realized this rn, they look like the small ones for lights. There's a wire to a light switch that's just connected with loose connection terminals. Its not pretty.

Would you leave a spur from a connection box in the floor?

Was this ever in the regs and if so why would anyone think this is a good idea?

thanks
 
You can take a spur from any part of a ring, this can be from a point, from a joint box or direct from the OCPD.

Any joint box will need to meet the regulations for the particular situation, so if it is to be inaccessible it would need to meet MF requirements or if it is outside it would need a higher IP rating.
 
Thanks. thought it always had to be from a socket. This does seem like a terrible idea though, makes fault finding difficult.

MF requirements? Not familiar with that term. As I understand the regs now (my copy is 10 years old btw), I thought they had basically said most existing typical brown round connection boxes were unsuitable if "inaccessible". carpet over floorboards, accessible? Think John Ward did a video i will rewatch.

Small aside, I have "accessible" connection boxes in my house. The side panel has fallen off the bath! That was a head scratcher, when the water went cold because the water slopped out, into the connection box, that fed the ring that the boiler was on. They put one there for the cooker too.

He has got all the plaster down, so it seems like a good time to sort things out.
 

Reply to Spur of midpoint of ring? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
1K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
860
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
630
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock