Discuss 2 x 3.68kW on two MPAN's or 7.36kW on one, Tale of a helpful DNO in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Worcester

-
Mentor
Reaction score
516
Interesting discussion today with WPD, (My favourite DN0 :) ) with regards to extending an existing 3.68kW system.

One pole, two overhead wires (single phase) two connections at the top of the pole to two seperate supplies, one terminates at the base of the pole, the other 10 m from the base, two seperate MPAN's.

Customer originally had one MPAN, one supply, requested the second one for an other building (workshop / sunlounge) in September last year, DNO agreed to supply and also said don't connect to the new supply until after 21st Jan becasue we're going to put new poles up and change the transformer (aka strengthening works).

We connected and post notified a 3.68kW system just before Christmas on the original MPAN and I got the connection approval letter at the end of last week. (Not quite like the black hole of SSE !! )

As customer wants to add another 3.68kW system, I called the area planner / engineer to ask him if it mattered to them which MPAN we connected the 2nd system up to as either would need a Stage 2 application and they both feed the same phase.

2 Interesting outcomes:
1) The transformer for the upgrade was delivered to site on Monday and then taken away today, when asked why, they said, because there's some PV been / being connected to the system and we need different / larger transformers ...
2) When discussing which MPAN to connect to, the DNO engineer was really concerned about voltage drop (rise), and I guess based on V=IR, the same cable with twice the current will have twice the voltage drop, so push up the generator voltages.... He was especially concerned about the drop between the top of the pole and the termination point at the consumers end, looking at the size of the incoming cables - I think I see why! Although 100A supply fuse and 25mm tails, the incoming is definitely smaller than the tails.. He was actually more than happy that we connect to the 2nd (new) supply, and even went so far as to say that so long as we don't commission it until after the 21st Jan,then we should just submit a post install (Stage 1) notification. However, because the owner could use the extra generated power, (the sun room / workshop will consume diddly squat when it's generating, and will need an EPC..) connecting both to the one (original) MPAN would financially more than make up for the small drop in Feed In Tarrif (FiT provider has already confirmed 2 x MPAN's = 2 @ full / <4kW rate), DNO engineer has now gone away to work out the implications of putting it all through one MPAN.

Notes:
1) All this without filling a form in yet
2) They are being as helpful and co-operative as any one could wish for.

Moral:
Talk to them, get them on your side and it's suprising what they'll do for you.
In this business it pays to make the DNO your friend.

Footnote:
Why do all our installs have twists, turns and complications like these?!!
 
Never found it easy to get a good contact within the DNO, so many of them seem to have one way phones.

Not sure if this is relevant to you situation but we have come across cases when 2 MPAN's are used but the FiT register sees both the MPAN's as related (on the ECO's database) as they are at the same point and has treated the 2nd registration as an extension from the first regardless of the different MPAN's.
 
As we are based in the Midlands all of our installs have been in WPD's patch and when I have needed to speak to them I have been able to speak to real people which has helped. I agree that clear communication (on the phone and making usre you understand what they are saying) is always a good idea. This was the gist of the guide to the connection of dist gen issued by the DTI many years ago.
 
as they are at the same point and has treated the 2nd registration as an extension from the first regardless of the different MPAN's.

That's why we spoke to the FiT provider, different MPAN's feeding different buildings (2 x EPC's) seemed to be the key point in our favour for 2 x <4kW. Though even now it is open to some interpretation.

One of the 'good' things to have come out of the full review is that people are now more interested in getting a system the right size for their use rather than what the FiT bands are.
 
Just finished a 40kw job on two storage units
20kw each unit (twin units)
4 mpans 10kw each 3ph
4 EPC
Building owned by one person
start to finish this has taken 4months, waiting for EPC to come back that was 4weeks then DNO application 6weeks, then had to remove heaters to comply, then EPC revisit 2weeks and to top it of bad weather. Nightmare. Commercial EPC are crazy
 
@Jason121 seems like a nice little job that, a nice weeks work :)
We love it! see my final sentence in the opening post - that's kinda what we expect. Our turnaround though from client saying 'go' to comissioning is usually less than 8 weeks, with EPC's, DNO Approvals and Full structural calcs, plus method statements, risk assements, There again, lost count of how many times we have the curved ball to cope with - every commercial job has one, can't think of a single commercial job that followed the text book! Quickest we've done was 4 weeks, when (nearly) everything went right.
 
I agree, WPD do seem to be the best.

I would echo your advise to give them a ring too. The connections guys seem to be the most helpful people at the DNO from our experience.
 
I would say WPD are the best we have dealt with as well. You ring them up to check applicatioin status and get given the engineers contact deatils who are dealing with your application. They even turned around a 50 kW application in 3 working days!
 

Reply to 2 x 3.68kW on two MPAN's or 7.36kW on one, Tale of a helpful DNO in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi everyone We have a little problem with a heating system on one of the projects (quite big house in south Kensington) and we are looking for...
Replies
14
Views
2K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K
Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock