Is a 20A 2.5mm radial sufficient for 2 sockets in a utility room? Will be a tumble dryer/washing machine plugged in and a spare socket used for a Hoover occasionally.
 
Sure, 2G is rated 20A with potential of 26A. The cct is already in place, just wondering my best method as customer wants to change the existing room to a utility and plug in washing machine and tumble dryer. Was thinking run a 2.5mm back to the consumer unit and make it a 32A ring. But thought it was a bit excessive for 2 double sockets?
 
Is a 20A 2.5mm radial sufficient for 2 sockets in a utility room? Will be a tumble dryer/washing machine plugged in and a spare socket used for a Hoover occasionally.
Typical ratings for washing m/c 2.2kW, tumble dryer 2.5kW, an old vacuum anything from 900W to 2kW!
You're around 20A with just the washing m/c and dryer, let alone plugging anything else in.
I don't thing the rfc idea is at all excessive in this case! Could always add another socket 🤪
 
If you are going to put in a return leg for the existing socket, why not put in a new radial instead, as too the Vacuum cleaner will it really be used at the same time as both the others?
 
If you are going to put in a return leg for the existing socket, why not put in a new radial instead, as too the Vacuum cleaner will it really be used at the same time as both the others?
The return leg can be installed in some surface trunking in the corner back to consumer unit to save chasing. A vacuum might not even be plugged in, just thinking worst case loading. Likely the other socket will remain unused.
 

Reply to 20A radial 2 double sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
748
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
If someone made a request to you, to install a new double socket that would be supplying power to a tumble dryer along a circuit that does not go...
Replies
12
Views
463
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
969
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
679

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock