Hi all,

I was called out earlier today to a house where a plumber was fitting a new mains electrics shower. He wanted to know if the existing cable was of a suitable size. I am a recently registered electrical contactor, however I hadn't come across this issue before. The cable was a 6sq pvc pvc. Houses were built in the 70s but cable wasn't as old, as they were brown blue and earth. However, I'm getting 230v across N+E, and 0v across L+E. Would I be right in assuming the house may not be neutralised?

Thanks in advance for all advice
 
Last edited:
It sounds more like reversed polarity which is very dangerous as (I think) ROI is like UK in that it has OCPD only in the L path and so if L & N are swapped you have no protection against faults to E.

AFIK the "neutralised" aspect is basically a local earth rod on the TN-C-S supply but @Risteard or @LastManOnline are the best to advise.

It could be a floating CPC leaking to L, but it is something you have to get professionally checked AS SOON AS POSSIBLE!
 
Hi all,

I was called out earlier today to a house where a plumber was fitting a new mains electrics shower. He wanted to know if the existing cable was of a suitable size. I am a recently registered electrical contactor, however I hadn't come across this issue before. The cable was a 6sq pvc pvc. Houses were built in the 70s but cable wasn't as old, as they were brown blue and earth. However, I'm getting 230v across N+E, and 0v across L+E. Would I be right in assuming the house may not be neutralised?

Thanks in advance for all advice
Apologies, I edited the previous post. I'm getting 230v across L+N and 230v across N+E. But 0v across L+E
 
The N is definitely missing.

0v from L to N means that there is a connection between the 2
but because N to E is at 230v it means that you must have a floating N

Edit,
after reading the last post, it may well be that you have a reversed polarity fault.
some proper investigation needs to be done with the house isolated from supply until you can be sure that the polarity and earth are ing god working order and the correct way round.
 
It sounds more like reversed polarity which is very dangerous as (I think) ROI is like UK in that it has OCPD only in the L path and so if L & N are swapped you have no protection against faults to E.

AFIK the "neutralised" aspect is basically a local earth rod on the TN-C-S supply but @Risteard or @LastManOnline are the best to advise.

It could be a floating CPC leaking to L, but it is something you have to get professionally checked AS SOON AS POSSIBLE!

Caught mention of 'neutralised' and completely missed the fact that 230V was present between N&E.
 
As above, but repeated to reinforce the message: If the polarity is reversed at the supply terminals or meter, no single-pole fuse or circuit breaker will offer any protection whatsoever against earth faults, and all circuits will be effectively fused at whatever the main fuse rating is. You might have 100A fusing on every single appliance and any minor fault could turn into a fireball. Hopefully it's only on that one circuit but it needs checking immediately.
 

Reply to 230v between N+E and 0v between L+E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
674
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock