Discuss 230v between N+E and 0v between L+E in the UK Electrical Forum area at ElectriciansForums.net

As @Lucien Nunes has pointed out you could see polarity reversal at any one of several places. Worst case is the supply point is reversed and so the supplier's earth/CPC permanently live. That ought to be very unlikely but should never be ruled out.

This is one case where a good non-contact voltage detector pen could be a life saver! If you find it suspiciously "volty" around the supply head, CU case (as @timhoward already warned about), etc, then call the electricity board immediately.

The whole house reversal is VERY dangerous as well, but more common and more likely to have happened when a meter was changed or CU installed and someone got the tails in the wrong way round.

Finally it might just be the one circuit that someone has managed to swap L & N, probably easier to do at a RCD/RCBO than normal CU, but still a bad thing to find.
 
. Would I be right in assuming the house may not be neutralised?
You can establish neutralising with 2 steps....

1) visually confirm the link from the ESB,s cutout to the main Neutral in your D.B.

2)Test its effectiveness by conducting a continuity test between the main Neutral and the Main earth.It should read "0.00 ohms"

I,m working in Cork today.If you want to cintact me ,feel free.
 
Hi all,

Many thanks for the replies. Those of you who said reversed polarity were correct. After much digging in the attic under floor boards I found a junction box where the polarity was reversed on load cable coming from the pull chord, cables very badly made off too might I add.
I haven't found out how long this man is without a shower, because I don't see how the previous shower would have worked either.
Either way, shower is now operational. I have offered to inspect the house at a discounted rate, as the owner is an elderly gentleman who lives on his own with very limited social contact.

Thanks again for all your help guys!
 
You can establish neutralising with 2 steps....

1) visually confirm the link from the ESB,s cutout to the main Neutral in your D.B.

2)Test its effectiveness by conducting a continuity test between the main Neutral and the Main earth.It should read "0.00 ohms"

I,m working in Cork today.If you want to cintact me ,feel free.
Thanks very much for the words of wisdom! And a particular thanks for the offer of help. Much appreciated.
 
Hi all,

Many thanks for the replies. Those of you who said reversed polarity were correct. After much digging in the attic under floor boards I found a junction box where the polarity was reversed on load cable coming from the pull chord, cables very badly made off too might I add.
I haven't found out how long this man is without a shower, because I don't see how the previous shower would have worked either.
Either way, shower is now operational. I have offered to inspect the house at a discounted rate, as the owner is an elderly gentleman who lives on his own with very limited social contact.

Thanks again for all your help guys!
With L-N reversed polarity it would have worked with the user unaware of the reverse polarity. Had the entire house been L-N reverse polarity then to the user everything would seem to be working as normal
 
Hi all,

I was called out earlier today to a house where a plumber was fitting a new mains electrics shower. He wanted to know if the existing cable was of a suitable size. I am a recently registered electrical contactor, however I hadn't come across this issue before. The cable was a 6sq pvc pvc. Houses were built in the 70s but cable wasn't as old, as they were brown blue and earth. However, I'm getting 230v across N+E, and 0v across L+E. Would I be right in assuming the house may not be neutralised?

Thanks in advance for all advice
Crossed polarity somewhere call an electrician
 

Reply to 230v between N+E and 0v between L+E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
674
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top