2 supply characteristics that can only be found out via enquiry to DNO

Ian I posted on this in another thread to the question above

The Pfc and the Ze can be measured or by enquiry
Frequency and voltage is nominal ,so these 2 cant be known by measurement only enquiry,city and guilds typical vague question
 
2 supply characteristics that can only be found out via enquiry to DNO

Ian I posted on this in another thread to the question above

The Pfc and the Ze can be measured or by enquiry
Frequency and voltage is nominal ,so these 2 cant be known by measurement only enquiry,city and guilds typical vague question

Wouldn't the type and rating of the fuse be one aswell seeing as you can't pull the fuse to 100% know the tye and rating?
 
If you look on the supply characteristics section on the test sheet in the fine print it says that you can only get nominal voltage and frequency from the supplier, just noticed it now. There was a question in Part B about the supply fuse or did I make that up?
 
I'm sure Q1 was what do you have to verify on an initial verification and Q4 was why do you carryout an initial verification or something like that. Seemed an overkill on the initial verification questions?
 
Wot about the Supply Transformer to MET for tt, tns, tncs? Did u start at Transformer i.e. transformer, supplies Line conductor.. etc, or start at MET i.e. MET, installations Earthing Conductor...?
 
The volt drop answer was 0.38x30Ax1.2=13.68v. Which is over 11.5v and exceeds the maximum volt drop. But I couldn't work out if the roller shutter was in a private or public installation as it was in a retail outlet but not part of the shop??????! This would change the max volt drop.
 
Our tutor told us the day before the exam that you no longer multiply by 1.2 now. Hope he was right or I am wrong on that one!
 
hi marnik have you maid it up because the formula for calculating the volt drop is Vd=(R1+Rn)xId
and on GN-3 said that on circuits supplying motors with high inrush starting current is allowed higher voltage drop and 1.2 factor is not mentioned.
 
There is different % of allowed voltdrop from a electrical installation that is in a public area than one it is a private area. Hope this solves your ???????????

Sounds like we are all being taught something different!
 
It's not areas it's distribution networks there are public distribution and private distribution ie if a factory has its own transformer in its own substation or public is if you are off a standard substation
 
There is different % of allowed voltdrop from a electrical installation that is in a public area than one it is a private area. Hope this solves your ???????????

Sounds like we are all being taught something different!

I suggest you have another think about that.

As far as I was aware the only deviation in the volt drop values allowed in the BS 7671-2008 concerns motors and is regulation 525.4 in the BRB. Now as the C&G 2391 based on the BS 7671 perhaps that is what you mean when referring to a roller shutter.
 
Q1 was something like this - an inspection of an installationis being done as part of an intial verification. What 3 conditions must be verified?

Q4 purpose of initial verifcation as per GN3
 
In a way you are both right App 12 has two for a public (DNO) system and two for a private supply. 525.4 is as stated in quote

The question as I remember was something like - a single phase motor is running slow and gets hot and it is believed it is a volt drop issue
1. calc vd if L1 & LN is 0.38 and motor load is 30A
2. does vd above meet regs
3. one course of action to be taken if vd is too high and why

I suggest you have another think about that.

As far as I was aware the only deviation in the volt drop values allowed in the BS 7671-2008 concerns motors and is regulation 525.4 in the BRB. Now as the C&G 2391 based on the BS 7671 perhaps that is what you mean when referring to a roller shutter.
 
Yes your quite correct there is different value in the appendix for private supplies such as generators and I did forget this , so the C&G may have thrown that one in, but never known them to use it before.

Thanks for reminding me.
 
Votage drop calculation formula= R1 + Rn x 1.2 x Ib
So in this case = 0.38 x 1.2 x 30
Voltage drop = 13.68v = 5.95 % DOES NOT COMPLY!!

1.2 is the multiplying factor to convert the resistance of a copper conductor at a temp' of 20 degrees C to a temp' of 70 degrees C.

The question gave resistances of R1 and Rn but did not say at what temperature. So why are you using 1.2 ??
 
1.2 is used because you have to take maximum operating temp of the cable when making this calculation. Otherwise when the circuit is in use and the temp of the cable rises the calculations and current carrying capacity will change. Worst case Scenario. Otherwise it would comply when not in use but possibly not when in use.
 
1.2 is used because you have to take maximum operating temp of the cable when making this calculation. Otherwise when the circuit is in use and the temp of the cable rises the calculations and current carrying capacity will change. Worst case Scenario. Otherwise it would comply when not in use but possibly not when in use.

1.2 is used to convert a 20 degree resistance reading to a 70 degree resistance reading. See p105 of GN3:

For examplea reading taken at 20 degrees C could be converted to an equivalent reading at 70 degrees by determining the correction factor obtained from p105:
(1 + 0.004 (amb temp - 20))

= 1 + 0.004 (70 - 20)

= 1 + 0.004 x 50

= 1.2 So this is the multiplying factor to convert 20 degrees C to 70 degrees C.

BUT THE IMPORTANT THING IS THE QUESTION DID NOT SAYWHAT TEMP THE READINGS OF R1 & Rn WERE TAKEN AT.
 

Reply to 2391-10 Written Exam - 01/12/11 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi Guys. Just wondering what people used to practice the written part of the 2391-52 exam? I have the iet exam prep book, which seems more geared...
Replies
4
Views
529
Hi Guys, I'm looking at booking myself on the 2391. Just wanted to see if anyone has ever done the course online and then done the 2 day exam. If...
Replies
5
Views
716
Hi all, ive found myself in a bit of a desperate situation here. I sat my compex 10 months ago and failed sections 01 and 04. I was meant to...
Replies
2
Views
9K
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
615

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock