- Reaction score
- 618
I have the OSG 16th ed and the two 17th ed GN3 (I cannot find my 16th Ed GN3)
The 16th ed test (in the OSG) and the 17th Ed:2008 (GN3) both say you may use the EFLI method if the rod is used in conjunction with an RCD
The 17th ed amd 1 GN3, has now removed this RCD requirement. This is what is new :cheesy:
Ah, now I see where you're coming from.
I can see why they changed it. Testing through a RCD will always give spurious results. Maybe this test was invented so that the novice always had the protection of the RCD if testing live, but then decided that anybody testing live should know what they're doing.
There is nothing new here, as I said before. Testing across a RCD is more likely to give overestimated results rather than referring to 411.5.2 and .3